Discuss 1st big job, would like some tips in the Industrial Electricians' Talk area at ElectriciansForums.net

S

scampy

Hello again all. I am about to to take on my 1st big job, so far i've added sockets lights ect but now i have the chance to do a rewire. It's a black canvas that a freind is renovationg so i have plenty of time to concentrate on doing a really good job.

I have some questions though, unfortunatly the part P course tought me the theory but has left big holes in the practice.

no1,
how far do you go with the 1st fix? my understanding is you place the cables and boxes but you do not attatche to lights and sockets.

do you go as far as setting up ganged lights and the attatching to junction boxes? He is unsure on what lights will be going in so i intend to uses junction boxes and take the switches from them, have i explained that right?

No2
How deep do you cut in. i'm going to attatch the cable directly to brick work under metal earthed protection. i'll then need to cut in the boxes. i guess i'm asking, how thick do i presume the plaster will be?

No3,
I think i know the answer to this. you do all the testing and inspection at the end of the second fix?

Cheers for your time
 
first fix would involve running all cables, conduit backboxes etc.
finished surface of boxes should be flush with finished plaster (about 5mm)
insp & test should be carried out progressively during erection
 
Hi Scampy,

Good luck with the job. I'm in a similar situation with being qualified as competent :)eek: *puts flame-proof suit on) but short on time-serving & experience.

ezzzekiel gave a useful response. If most of your back boxes are going to be 35mm, you could avoid the messy brick chasing by asking the plasterer to apply a 30mm render coat - any electrician-----plasterers out there have preferences on the first-fix electrics set out? Prefer capping or not bothered?
Watch out if you're thinking of using grid switches, the back box required may be 40mm - best to check with manufacturer.

Inspect and test all the time - it gives you the practice! :D

No.15
 
Hi no15

you can take your flame suit off (for me anyway) personally I think lifes too short to worry about other peoples qualifications etc but I do worry about electricians going out on their own with no experience as I know how much electricity can hurt (first hand...thats another story).

Just wondering what courses deem you as qualified and competent??
 
....could avoid the messy brick chasing by asking the plasterer to apply a 30mm render coat....

I'm sure that any plasterer will be quite happy to double the thickness of the render & skim (and therefore his materials costs) just to please a bone idle electrician who can't be arsed to chop his boxes in. I can see it now; he'll smile down benevolently at you, ruffle your hair like the cheeky little scamp you are then tell you to "---- right off!" He may then start pointing and laughing.
 
Hello Montybaber,

I've taken and passed the VRQ Level 2 Domestic electrical installer part p course, which confirms I'm competent to carry out and self-certify domestic electrical work. It also means that any work I do will comply with Part P of the Building Regulations (and also Parts A, B, C, E, F, L, and M ! where pertaining to electrical installations). I have a great healthy respect for electricity and, unlike some gung-ho persons, would not attempt work beyond my ability or comprehension.

Now that I've outed myself, I can't ask stupid questions any more! :-(

I'm sure that any plasterer will be quite happy to double the thickness of the render & skim (and therefore his materials costs) just to please a bone idle electrician who can't be arsed to chop his boxes in. I can see it now; he'll smile down benevolently at you, ruffle your hair like the cheeky little scamp you are then tell you to "---- right off!" He may then start pointing and laughing.


Good point. Though I'd rather plaster than chop - there's something serene about floating and waving about as opposed to gritting teeth and fighting the wall ;).
 
Last edited by a moderator:
Hello Montybaber,

Level 2 Domestic electrical installer part p course, which confirms I'm competent to carry out and self-certify domestic electrical work.

really cant see how these courses make people competent, not even years of college does that - its hands on, day in day out that makes a good spark...

take your time, check everything as you go, stick to regs and if not sure ask (but dont ask the plasterer) :)
 
Hello Montybaber,

I've taken and passed the VRQ Level 2 Domestic electrical installer part p course, which confirms I'm competent to carry out and self-certify domestic electrical work. It also means that any work I do will comply with Part P of the Building Regulations (and also Parts A, B, C, E, F, L, and M ! where pertaining to electrical installations). I have a great healthy respect for electricity and, unlike some gung-ho persons, would not attempt work beyond my ability or comprehension.

Now that I've outed myself, I can't ask stupid questions any more! :-(



.
passing the course does not make you:

A:- competent

or

B:- mean that any work you do will comply with relevant parts of the building regs

How can it? It means you have an acceptable understanding of what is REQUIRED to meet the laid down standards

It is no measure of your ability (or indeed willingness) to meet the those standards and rules

I am not saying you are not competent - I hope you are:)
I am not saying you dont (try) and comply with the building regs (i hope you do):)

but we want to do, and what we CAN do, are not always the same thing - and no certificate will prove otherwise

(and i speak as tutor who has taught many, many Domestic Installer VRQ courses):rolleyes:
 
Oh yes dont upset the plasterer, at a job in fleet where I got talking to the plasterer during the first fix (got on fine with him), he tells me that he is waiting for a complaint from sparks off another job...story goes;

Sparks during first fix, caused an argument with the plasterers boy (ended up bullying him beyond site banter), the lad tells the gaffer who comes over to the job removes his boys off the site before fisticuffs ensue & agrees with customer to come in later in the week after the sparks have completed 1stfix & cleared off.

The plasterers go in ............... oh dear cables for downlights are now short & a few lugs are missing off backboxes + ring legs at outlets are now a tad shorter (we know how much of a pain in the arris that is).

DONT P*** THE PLASTERER OFF.


Afternoon Shakey hows things in your neck of the woods
 
Last edited by a moderator:
passing the course does not make you:

A:- competent

or

B:- mean that any work you do will comply with relevant parts of the building regs

How can it? It means you have an acceptable understanding of what is REQUIRED to meet the laid down standards

It is no measure of your ability (or indeed willingness) to meet the those standards and rules

I am not saying you are not competent - I hope you are:)
I am not saying you dont (try) and comply with the building regs (i hope you do):)

but we want to do, and what we CAN do, are not always the same thing - and no certificate will prove otherwise

(and i speak as tutor who has taught many, many Domestic Installer VRQ courses):rolleyes:

Shakey, I understand what you say, the course doesn't make me competent - that's up to me. I follow the rules - which is why I took the course in the first place. Here's the description of the course I took:
'The fundamental objective of this qualification is to enable candidates to develop the competences to allow them to carry out electrical installation work in dwellings. It references only those skills necessary to carry out domestic electrical installation work in accordance with standard circuit arrangements. The necessary competences to carry out the inspection and testing of newly installed electrical installation work in dwellings are also included in the qualification. The successful candidate will be considered to have achieved competence, specifically as a Domestic Electrical Installer. They will not be considered to have achieved the recognised competence required to operate as an electrician.'
Not gonna say the 'c' word anymore, *sulk
..
..
..
can I say I'm a crap domestic electrical installer? Then I can ask stupid questions again.

:D:D:D
 
Hi scampy

Do not use junction boxes on a rewire. You say you have a blank canvas and it is your first big job, realistically there should be no need for junction boxes. Do not get into bad habits now they will come back to bite you in the bum later on.
 
Hi mate , Ring main ~ 1 x up 1 x down , run in 2.5mm t+e , depending on what is happening with the walls will dictate how much chasing you have to do , if the walls are getting dot an dabbed (plaster boarded) , i generally chase skt boxs in 10mm deep max as that's all that is required .... if the walls are not getting boarded, just a skim over existing plaster then you will need to chase skt boxs flush with original plaster ( use 25mm skt boxs ) not 35mm or 45mm
once you have fixed your skt boxs in place , run your ring main in, for the chases down the wall use 25mm oval plastic conduit ..

same goes for the lighting circuits x1 up x 1 down , just have your feeds and sw wires sticking out the ceiling through a nog-ins , with sw wires in the switch box's as above

don't forget your gas and water 10mm earths

plastic oval conduit all your cables down to were your f/board is going

Get your self some new wood bits to drill the joists 20mm + 25mm ...

Screw fix is good for gear

Why use earthed metal capping ? use plastic oval conduit and fit a duel split RCD board

Hope this helps getting you started

Ste
 
Last edited by a moderator:
hiya scampy

hiya scampy in response to your questions.
1.yes, you install all cabling & flush boxes as a first fix, i personally wouldnt use joint boxes because they should be left accessible for future inspection, use either the loop in system (3 plating) for the lighting or alternatively loop your cables behind the switches thus leaving only one cable to your light position, but be aware that with the connections behind a switch you will need at least a 25mm deep switch box.
2. with reference to depth of boxes, find out how the plasterer is finishing the walls, if he is wet plastering the walls you will need to sink in boxes so they sit approx 12mm out from the existing brickwork, if he is drylining with plaster board called (dotting & dabbing), you can usually fix 25mm deep boxes directly to the wall.
3.testing, yes you do this at the end of the 2nd fix, but keep looking visually during 1st fix for any mechanical damage that may have ocurred.


I must say be very careful with everything that you do follow the regulations and if you are unsure take proffesional advice from an experienced electrician, as you are inexperienced i would also wonder what qualifications/status you have to certify your own work.
As a self employed spark of 20yrs with 35 yrs in the trade i had to do all the courses (16th & 17th edition regs & testing/inspection courses) & join the N.I.C.E.I.C. to self certify my work.

So be very careful, be sure that you are qualified to certify your work and remember you will be solely responsible for the work you do, Oh & good luck.
dave
 
Last edited by a moderator:

Reply to 1st big job, would like some tips in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Just had a simple kitchen light not working job, one of the fittings with the 4 spotlights on it. Took the fitting down to check if there was...
Replies
7
Views
948
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
So a quick catch up so you can get an idea… I was asked to do a job for another electrician, as he is too busy. I’m busy myself but said I’d...
Replies
18
Views
2K
I am an experienced electrical engineer consultant in building services, and I am looking to expand my professional horizons by taking on side...
Replies
1
Views
494
Hi all, Just wondering what the general situation is with other people on smaller jobs, do you give a quote or estimate to the client before you...
Replies
6
Views
947

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock