Discuss 2.5 spured of a cooker supply in the Electrical Appliances Forum area at ElectriciansForums.net

TJC1

-
Reaction score
6
Carrying out an EICR today.

Found a radial 6mm supply, 32a, to the cooker, with a 2.5 spur off to a double socket.

Debating whether to mark down as an observations. In my mind its the same as a spur of a 32a ring main??

Thoughts please
 
agree. highly unlikely that the 6mm will be overloaded. ifit's ref.C, then it's good for 47A and it's protected by a 32A MCB. the socket is unlikely to pull over 20A, so the 2,5mm also is safe.
 
Socket rated to 13amps, cooker diversity applied so unless the circuit can be overloaded and the spur is adequately protected for fault protection it's ok
 
will that cause a fire? needs a ferrous cooker isolator. :p
 
Sorry the Zn neutral loop impedance as to ensure the cable can withstand a short circuit fault as being supplied with a 6mm could have quite a low impedance resulting in a higher fault level.
 

Reply to 2.5 spured of a cooker supply in the Electrical Appliances Forum area at ElectriciansForums.net

Similar Threads

Good Evening. I’m currently carrying out an EICR. I have a cooker circuit radial with a 32amp mcb fed from and RCD split board. There is a 45amp...
Replies
14
Views
788
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
611
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
608
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
743

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock