I'm not sure there is a regulation stipulating max length. I think the 3m length reg you are thinking of is specifically for pendants with smaller flex.

So a scenario: you need to install an extractor fcu and the ONLY circuit you have accessible to take it off is the cooker on a 32A breaker. Does that mean you take it from the cooker point in 4mm+ to the fcu, or would you take it in 2.5?

With this scenario I'd say it would be absolutely fine to run a 2.5, the current of an extractor fan would be minimal and a fraction of what 2.5 can carry so overcurrent protection isn't an issue. And the fcu would have an appropriate fuse [probably 3 amp] to protect the fan and its internal circuitry. As far as terminating a 2.5mm cable in the same terminals as 6mm there's no problem as long as it's done carefully.
 
In my opinion for whats it worth, I am sure you cannot reduce the cable size without down rating the mcb, therefore in this instance a fused spur should be connected in circuit between the last 4.0mm fed socket and the 2.5mm fed socket.
 
In my opinion for whats it worth, I am sure you cannot reduce the cable size without down rating the mcb, therefore in this instance a fused spur should be connected in circuit between the last 4.0mm fed socket and the 2.5mm fed socket.

Not entirely true. Otherwise busbar systems wouldn't work. Daz
 
As somebody said before, its shown as an example in figure 15B, so why is C2 or wrong or poor practise?

Fig 15B sure does show it, no question. My take is ...
Fig refers to 433.1, but 433.1 doesn't lead me to think 4mm to 2.5mm is ok. But reading on to 433.2.2, it seems to say ok < 3m, with a couple of conditions.
 
The op asked for opinions, mine you have two final circuits from a single protective device one of which reduces in csa. This circuit which reduces in csa is ad hoc with absolutely no thought for BS7671, the chance of further add ons with the same sized reduced cable is high.
 
I don't agree with not having a circuit such as this because people might add further sockets on in the future. If you go with that theory then you would never have spurs from sockets at all, because someone might come along and spur from the spur. No difference - both cases have a length of 2.5mm feeding a socket. Daz
 
Th
I don't agree with not having a circuit such as this because people might add further sockets on in the future. If you go with that theory then you would never have spurs from sockets at all, because someone might come along and spur from the spur. No difference - both cases have a length of 2.5mm feeding a socket. Daz
The chances of this so called spur being installed as per BS7671s "Guidance" is zero, I would feel it is open to further abuse, that is how I view it.
 
Fig 15B sure does show it, no question. My take is ...
Fig refers to 433.1, but 433.1 doesn't lead me to think 4mm to 2.5mm is ok. But reading on to 433.2.2, it seems to say ok < 3m, with a couple of conditions.

interesting, 'cause its clearly okay in App. 15. perhaps the intention is 433.3.1 (ii), where a single outlet is deemed "not likely to carry overload current" ?
 
Is it me or is this getting all out of proportion?
No its not necessarily how any of us would install it, but its not likely to be an issue either. Its highly unlikely the circuit would be overloaded during normal use, and any electrician worth his/her weight would not install another spur off that socket.
I would maybe just make a note on the report and possibly give it a C3/C4 if I felt the installation required it.
 
Is it me or is this getting all out of proportion?
No its not necessarily how any of us would install it, but its not likely to be an issue either. Its highly unlikely the circuit would be overloaded during normal use, and any electrician worth his/her weight would not install another spur off that socket.
I would maybe just make a note on the report and possibly give it a C3/C4 if I felt the installation required it.
By coincidence just finished doing a school EICR, existing circuit has a spurred two gang and just recently another has been connected from it. All fine according to "electrician" who also left a MWC on site.
 
By coincidence just finished doing a school EICR, existing circuit has a spurred two gang and just recently another has been connected from it. All fine according to "electrician" who also left a MWC on site.
That's down to that bad boy then. Most things plugged into sockets nowadays aren't 2kw electric fires.
 
Just wondering what folks would do if you came across this on your travels. 4mm radial sockets circuit, on 32A MCB. Two branches from the CU, one supplying 6 double sockets, wired entirely in 4mm, so fine. The other branch consists of a 1m run of 4mm to a double socket, then around 5m in 2.5mm cable on to a second double socket.

The question is, who would be happy to leave this arrangement in place, and who would downgrade the breaker to 20A? I would say it's ok, as the 2.5mm can't be overloaded as it feeds only one double socket, just like an infused spur off a ring.
what if somebody plugs a 4 gang into the last socket??? easily overloaded then sir
 
By coincidence just finished doing a school EICR, existing circuit has a spurred two gang and just recently another has been connected from it. All fine according to "electrician" who also left a MWC on site.
Things can happen, no doubt. But it is very unlikely that during normal use in a domestic property that the socket in question would be overloaded. If some idiot decided to extend off that socket then that's their responsibility. No one can foresee all events.
Like I said non of us would install the socket in this manner, and yes in exceptional circumstance there could be a chance it gets overloaded. As I said I would asses the install, make a note on the report and then perhaps code it accordingly if I felt it was going to be a potential problem.

Its easy to fall into the nanny state mentality, stifled by bureaucracy. This doesn't mean ignoring potential hazards, but rather accessing the situations to determine the severity. But we cannot wrap people up in cotton wool, they have to take some responsibility for their own welfare.
 

Reply to 2.5mm on 32A MCB in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, just helping someone out and apologies for the long winded post. Would like install a couple of weatherproof double sockets on the patio. 1...
Replies
3
Views
711
Ok i may get slated for this one but here goes; A bit of background info first. Its been a while since ive looked at my iee regs, and ive not...
Replies
12
Views
2K
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
595
Hi I've got a job that i've been asked to quote for and i'm struggling with how to do it the best way. It's a summerhouse and the customer only...
Replies
17
Views
3K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock