Afternoon men (already bored of the football!)

for radials circuits that are to be installed as 100,101,102,103-table F6 is your friend!

but when it comes to ring circuits wired in 2x 2.5mm on a 32amp it always confused me a little!

-I know that 20amps per leg is the magic number- so the above example would be fine as 2.5mm ccc as 100 is 21amps

could someone point me in right direction as to where the magic 20amps per leg comes from pretty please
 

Reply to 2.5mm ring ref method 100 in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So the CCC of 2.5mm is 27 amps clipped direct. So a ring would be 54amps altogether, yet is put on a 32 amp breaker. I understand that the legs...
Replies
13
Views
9K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Afternoon all, A quick EICR question. I have found a Ring Final Circuit that has been run in 1.5/1mm twin and earth. It is RCD protected and OCPD...
Replies
24
Views
4K
S
Bit nervous about putting this on the open board, normally stick to the trainee section. Hope i can get some help. I have recently qualified so...
Replies
4
Views
2K
Ste69
S
Hi again, 2.5 TE cable installed within fully insulated partition walls which i would of thought is now pretty mush standard now on...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock