Discuss 2core swa, not earth load end.. TT in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

robo83

-
Reaction score
40
Hi,

Been to a job with a 2core swa supplying the garage.. The swa has been glanded inside house to CU. But the other end in the Garage has had the swa run in plastic conduit with no gland on the swa so unable to test r1/r2.

However the garage has its own earth rod. So technically the swa is earthed from the house end, with the garage having its own earth rod.

The garage earthing TT is 37.0ohms, would I note this down as the garage r1/r2 circuit. Accepted with the 1667ohms as rcd?
 
Did you mean to quote the OP Pete :(
Not sure what you are getting at Middy, just trying to say to the OP that r1 and r2 are readings for r1 Live and r2 Earth as a single conductors, I thought he was meaning R1+R2 or am I getting tangled up somewhere?
 
Robo83, can you not get a croc clip on the armouring at all at the garage end? Then you could measure r1 + r2 this way? Midwest and pete, if that was possible, is that allowed?
 
I dont follow...
You are trying to measure the loop of the L and E conductors correct? Which will give you a resistance reading noted as R1+R2 not r1+r2 a small thing but end to end reading r1 r2 and rn are recorded as RFC readings only, and are end to end readings of the L.N and cpc, get the basics wrong and other things will be wrong as well. Of course if you are insulating the armoring from the garage end why would you try and trying to measure the R1+R2 of the distribution cable.
 
Last edited:
Robo83, can you not get a croc clip on the armouring at all at the garage end? Then you could measure r1 + r2 this way? Midwest and pete, if that was possible, is that allowed?

Hum.... Not sure what that would achieve.... Think about what you are testing
 
the swa earth is not part of the garge earth so R1/R2 is gonna be between L and the Rod E. If I read you right?
My thought is the garage supply is a circuit off the main db (house CU) and this would have its own loop impedance from the SWA armour, which is its CPC. Then the sub board (garage CU) and the final circuits are the TT bit (?) .
 
He is trying to verify earth continuity to the armour of the cable which is not accessible as it is contained within pvc conduit to isolate it from the TT, this earth continuity is applicable to the circuit from the house and nothing to do with the TT.
 
yeh but is it a circuit or just a piece of cable? Where is the loop hah!
Well if it ain't a circuit how does current / fault current flow in it? Being creative, I'm thinking it's a >32A distribution circuit with a 5 or 1 sec disc time from 411.3.2.3 or .4 - at least it would be if I'd done it in 10mm :)
 

Reply to 2core swa, not earth load end.. TT in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
405
Hi All, I own a country Villa out in the Spain countryside. Was having problems with water pressure so local tradesmen advised to get a water...
Replies
14
Views
973
Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
483
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock