Discuss 3 phase low voltage?? in the Industrial Electricians' Talk area at ElectriciansForums.net

Bsharp

-
Reaction score
22
Hi all I was called to a job this morning where the 3 phase supply was showing low voltage on two phases? The voltages where L1-245v
L2-110v
L3-135v
could anybody give any possible reasons why this was the case? I have handed it over to supply company as I thought must be a fault on their side
thanks for any input.
 
Presumably you meant to say 235 between L1 and L2? In which case I'd be inclined to say that the fault is indeed external and that it is on the L2 supply, possibly a high resistance connection, or something more sinister.
 

Reply to 3 phase low voltage?? in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Anyone come across this before? I was asked to do a Zs on a 3ph surge device; L1 was around 6 ohm, L2 & L3 around 0.11. Wired in singles from a...
Replies
1
Views
426
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
529
hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
273
I know the effect of a lost neutral (floating neutral) on a 3 phase system, and the theory of why the line voltages can vary. However, I have...
Replies
1
Views
726
Hi, I am looking for a connection diagram or sugestions for a 2.2Kw single phase motor to drive a compressor. The spec plate shows that it can be...
Replies
5
Views
733

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock