Discuss 3 phase question in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
4
hi guys
can someone explain to me this
a 3 phase supply to bungalow ok
one phase to house ok live
neutral& earth in henley blocks in meter box

neutral to 3phase meter from henley block

we have l1 l2 l3 lives to tpn 100amp switch fuse ( no neutral )
earth connection via earth block

from there we have a 16mm 4 core swa ( black ,red ,blue & yellow)
black --l1 fuse
red-- l2 fuse
blue--l3 fuse
yellow -- earth to henley block

thus feeds a 3phase board in workshop
No neutral to it.

1..???? is why is there no neutral to it
its not connected to earth
swa at cu is bonded at the armourings back to earth connection in board
and not at tpn ( discrimination)

2..??? why does all the 3phase equipment still work without a neutral

i am having to update a single phase cu to a 6 way to accomodate a solar pv 9.9kw system
luckily its got a 10.mm feed to it.

thanks
jon
 
hi guys
can someone explain to me this
a 3 phase supply to bungalow ok
one phase to house ok live
neutral& earth in henley blocks in meter box

neutral to 3phase meter from henley block

we have l1 l2 l3 lives to tpn 100amp switch fuse ( no neutral )
earth connection via earth block

from there we have a 16mm 4 core swa ( black ,red ,blue & yellow)
black --l1 fuse
red-- l2 fuse
blue--l3 fuse
yellow -- earth to henley block

thus feeds a 3phase board in workshop
No neutral to it.

1..???? is why is there no neutral to it
its not connected to earth
swa at cu is bonded at the armourings back to earth connection in board
and not at tpn ( discrimination)

2..??? why does all the 3phase equipment still work without a neutral

i am having to update a single phase cu to a 6 way to accomodate a solar pv 9.9kw system
luckily its got a 10.mm feed to it.

thanks
jon
ballanced loads mate...motors.

however...just looking at what you have decribed as L1 L2 & L3...

since when has L1 been black?
 
it should be

red=L1

Yellow=L2

Blue=L3

so something not right here...unless its just a case of someone not following the colours...or a phase reversal at the intake...

have you done a phase rotation on it?
 
Looks like the 3 phase supply was installed just for 3 phase machines/motors ,( no neutral required on 3 phase motors )

The 4 core swa is not wired correctly , but I suspect it tallies at both ends also,,
 
theres a sub feed from house cu to a workshop single phase to power lights sockets
ta
jon

- - - Updated - - -

theres a sub feed from house cu to a workshop single phase to power lights sockets
ta
jon
 
It looks like there was an original single phase supply , and then had 3 phase installed at a latter date, you see this a lot ,,,
 

Reply to 3 phase question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, I have been asked to pull in some new 3 phase supplies for 7 new welders which do not require a neutral connection. The client has...
Replies
4
Views
685
Anyone come across this before? I was asked to do a Zs on a 3ph surge device; L1 was around 6 ohm, L2 & L3 around 0.11. Wired in singles from a...
Replies
1
Views
427
Hi all. Yesterday I wired in my 3 phase compressor to run off our 53kva generator. I just need to know which colour cable is for which phase as...
Replies
13
Views
2K
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
656
I know the effect of a lost neutral (floating neutral) on a 3 phase system, and the theory of why the line voltages can vary. However, I have...
Replies
1
Views
730

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock