Circuit Info

32a B RCBO Feeding a Combi Boiler through a FCU in the airing cupboard of the bathroom.

Tested at 1/2 Passed tested at 1 > passed reading Oo 20.5 and 180o at 21.3

When testing at x5 the RCBO is tripping but my meter (kewtech KT63) is showing fail >50v

Im assuming that this is because it it requiring greater than 50v to operate

I have tested:-
at the terminals
FCU
At the terminals with live disconnected
" " " " " " " neutral disconnected

all other RCDs (2 in total) in the CU have passed with x1 29.6 & 31.4 and x5 26.8 & 22.3

It is a TT system and the Ze is 81.9
Zs of all other circuits are between 82.1 and 84.7

Have i missed something? or is the RCBO Faulty
 
32a RCBO Failing 5x with >50v showing

Is it just me or are the zs' a bit low once you take into account the ze of 81.9, either that or very good readings, that's makes the R1+R2's really really low
 
Re: 32a RCBO Failing 5x with >50v showing

Is it just me or are the zs' a bit low once you take into account the ze of 81.9, either that or very good readings, that's makes the R1+R2's really really low


parallel paths through bonding and extrraneous metal pipes.
 
No the meter is telling you that the touch voltage in the premises is more than 50 volts when you are putting 150mA INTO THE CCT so it is aborting the test. What is the ZS reading for this circuit as it sounds like a failure of the CPC so a high EFLI ! !
Hi

Circuit Info

32a B RCBO Feeding a Combi Boiler through a FCU in the airing cupboard of the bathroom.

Tested at 1/2 Passed tested at 1 > passed reading Oo 20.5 and 180o at 21.3

When testing at x5 the RCBO is tripping but my meter (kewtech KT63) is showing fail >50v

Im assuming that this is because it it requiring greater than 50v to operate

I have tested:-
at the terminals
FCU
At the terminals with live disconnected
" " " " " " " neutral disconnected

all other RCDs (2 in total) in the CU have passed with x1 29.6 & 31.4 and x5 26.8 & 22.3

It is a TT system and the Ze is 81.9
Zs of all other circuits are between 82.1 and 84.7

Have i missed something? or is the RCBO Faulty
 
Have you tried another RCBO on that cct & if so did that trip in 40 ms or under ?

For touch voltage to attain 50 volts or over on 150 mA you would need a ZS of 333 ohms or more ! 50/0.15 !
 
Not another rcbo no. However there are two RCD'S in the CU which passed with flying colours. I've sorted out a replacement for the rcbo will be collecting it tomorrow so il check back then.

I've disconnected everything from the CU now except from that rcbo and the main switch and it's still failing so it must be the rcbo
 

Reply to 32a RCBO Failing 5x with >50v showing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

S
Hello, I am a diyer doing my own board change shortly (paying a premium for the honour to BC) and have a problem either with my tester or...
Replies
14
Views
2K
T
Hiya Guys, I hope there is someone out there who can answer my problem. I'll do my best to explain my situation. Right then - I have been given...
Replies
17
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock