Natt

I've been asked to inspect a shop and have found 4x 32 amp ring final circuits supplying socket outlets, all wired in firetuf 1.5mm twin and earth.
Actually all the circuits are wired in this stuff, there must have been a deal on at the wholesalers..
My concern is does this comply with 421.1.103 as it's not micc but from what I can find the current carrying capacity of the cable is not less than 20A?
Also the three phase GE board is filled with 6kA mcb's, I was told they should be 10kA but can't find a reg for this.
Measured Line to neutral Ipf is 2.62kA
If these are deviations then my next question would be about codes for the Periodoc form, but I should probably ask that in the Inspection& testing section ;)
 
It's 433.1.5

The ring finals are certainly non compliment circuits and as such require improvement. Without any more information I'd be opting for a code 2.

As for the 6kA MCB's, they seem fine, even after doubling the 2.62kA PSSC Line to Neutral figure for PSSC phase to phase.

This is from GN3:

Where a service cut-out containing a cartridge fuse to BS 1361 type 2 supplies a consumer unit which complies with BS 5486-13 or BS EN 60439-3, then the short circuit capacity of the overcurrent protective devices within consumer units may be taken to be 16 kA.

Fault currents up to 16kA
Except for London and some other major city centres, the maximum fault current for 230 V single-phase supplies up to 100 A is unlikely to exceed 16 kA.

The short-circuit capacity of overcurrent protective devices incorporated within consumer units may be taken to be 16 kA where:
-the current ratings of the devices do not exceed 50 A
-the consumer unit complies with BS 5486-13 or BS EN 60439-3
-the consumer unit is supplied through a type 2 fuse to BS 1361 :1971 rated at no more than 100 A.
 
Last edited by a moderator:
To my mind, if the current carrying-capacity of the 1.5mm² firetuff is greater than20A after all correction factors have been applied, then it is fine.
The 6kA MCBs are fine, it's usual in commercial/industrial installations to use 10kA, but if the PFC is less than 6kA, there's no need for 10kA.
As far as I'm aware, it is only Type tested Distribution Boards, refered to as Consumer Units, which are rated at 16kA. All other types are not rated, and the rating will be based on that of the lowest rated device which is installed.
In this case, most probably 6kA.
 
Last edited by a moderator:
Thank you for the replies. The reg in the amended BS7671 is 433.1.103 my mistake.
There are no correction factors needed as far as I can tell, but I think I should list it on the Periodic as at least a code 3, as the next spark to inspect it will no doubt have a different opinion from whatever I say!
 
Thank you for the replies. The reg in the amended BS7671 is 433.1.103 my mistake.
There are no correction factors needed as far as I can tell, but I think I should list it on the Periodic as at least a code 3, as the next spark to inspect it will no doubt have a different opinion from whatever I say!

Don't list it as a 3, it doesn't need 'further investigation', list it something like 'ring final circuits A, B, C and D are wired in 1.5mm 'Firetuf' however there is still adequate current carrying capacity'.
In the defect code box, enter N/A.

Note, I'm assuming there is adequate CCC.
 
I think I will need to return to site and get more details of the cable used and find the manufacturers website, hopefully then I will be able to determine if the CCC is adequate.
 
Just another angle to approach this problem from, due to higher operating temperatures the cable can run at - it may have a higher than expected ccc, say 90c operating temp for example; but this aspect may be affected by the equipment, mcb's etc connected to the wire which may have a 70c rating thus derate the handling temp and de-rating the ccc from manufacturers tables.
Consequently this could mean its a fire hazard at its termination points, what you need to do is derate the cable to 70c and recalculate the ccc from this.
 
'firetuf 1.5mm twin & earth' ??Do you mean FP cable or low smoke t&E ?I get FP 1.5mm to a max of 19.5A !So the 32a MCB to big.
It all depends on the reference method.
19.5A is reference method C, with a conductor operating temperature of 70ºC, and an ambient temperature of 30ºC.
With reference method E, the CCC is 22A.
 
I know it's a ring, so there for on his 32a MCB he would need a cable capable of carrying 20amps would he not. Spinlondon you could be correct I would have to check, but I can bet that it's not all installed in ref E
 

Reply to 32A ring circuits wired in 1.5mm firetuf in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
A really simple question. I'm sat here with my coffee and getting confused by it! 7.4kW EVCP. Would I fit a 32A or 40A RCBO? Not concerned with...
Replies
8
Views
6K
We own a small, one bedroom flat (built 1989). An EICR inspection raised three C2 observations and recommendations: (A) The shower cable, and...
Replies
8
Views
4K
Hi All Just looking for a 2nd opinion on cable sizing / breaker for a old cooker. The customer has had a 'Cooker Engineer' out to advise that...
Replies
7
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock