I've been asked to inspect a shop and have found 4x 32 amp ring final circuits supplying socket outlets, all wired in firetuf 1.5mm twin and earth.
Actually all the circuits are wired in this stuff, there must have been a deal on at the wholesalers..
My concern is does this comply with 421.1.103 as it's not micc but from what I can find the current carrying capacity of the cable is not less than 20A?
Also the three phase GE board is filled with 6kA mcb's, I was told they should be 10kA but can't find a reg for this.
Measured Line to neutral Ipf is 2.62kA
If these are deviations then my next question would be about codes for the Periodoc form, but I should probably ask that in the Inspection& testing section
Actually all the circuits are wired in this stuff, there must have been a deal on at the wholesalers..
My concern is does this comply with 421.1.103 as it's not micc but from what I can find the current carrying capacity of the cable is not less than 20A?
Also the three phase GE board is filled with 6kA mcb's, I was told they should be 10kA but can't find a reg for this.
Measured Line to neutral Ipf is 2.62kA
If these are deviations then my next question would be about codes for the Periodoc form, but I should probably ask that in the Inspection& testing section