Came across a 2.5mm fp200 4 core cable used as part of a ring today, am I right in thinking this isn't an acceptable method as there will be only 1 earth wire in the cable ??
 
It has been used to extend the ring in part of a shop area mainly supplying pc's. There is a joint box with the 2 ends of the ring which are 2H2.5 mi's and the 4 core fp.
 
So it's being used to carry both halves of the ring in one cable?

Then as I can see it you have two problems, one being that the cpc is not in a ring and therefore not compliant and the other being that fp200 offers none of the protection characteristics of mi and so is almost never suitable as a suitable means of extending such a circuit for normal lighting/power installations.


Sent from my iPad using Tapatalk
 
Thanks, When you say offers none of the protection characteristics what exactly do you mean by that ? Do you mean if it is designed for MI then FP doesn't meet the design criteria that MI would give ?
 
You will have a 2.5mm^2 cpc then (not a ring cpc).

However if I am understanding the setup correctly then you don't have a ring on either of the live conductors emanating from the adaptable box either but rather parallel conductors.
 
Thanks, When you say offers none of the protection characteristics what exactly do you mean by that ? Do you mean if it is designed for MI then FP doesn't meet the design criteria that MI would give ?

I mean it does not have the same mechanical, thermal or electrical protection. The mi will also have a higher current rating, different temperature rating, different volt drop and a much bigger cpc
 
Ok, everything is clipped direct onto a block wall and is only about 5 metres of the 4 core used so there is still probably adequate protection for what you mention but I definitely agree with the Earth wire issue.
 
Why is the original in MI cable?

Is it a spec'd requirement on the original design i.e. Council property where higher durability and lower maintenance, maybe the tenants etc got in their own Electrician who side stepped any requirements additional to the regulations.

Been a shop may have meant Building Control and fire safety have specified MI is used and this needs to be looked into as the previous 'electrician' may have undertaken work breaching BC requirements.

Agree with others regarding the earth, bad design at the very least even if Zs is still met.
 
Last edited:

Reply to 4 core fp200 ring circuit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
Replies
2
Views
257
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
407
Carrying out an EICR and came across a ring final circuit wired to the first of six metal clad sockets in 2.5mm 5 core SWA. Obviously 2 cores for...
Replies
5
Views
922
Hello, I am a trainee electrician just starting to get into doing cable calculations. I understand them when it comes to a radial circuit but get...
Replies
5
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock