I was chatting with a PAT tester who mentioned that he would fail 4-way extensions where the flex had been trunked and the client was using them with appliances drawing 13 amps. His reasoning was that the trunked flex should be de-rated. Would you agree with this?
 
Most four way extension lead ends have instructions for connecting to a 13A plug top. I will always note this on an EICR if they are hard wired to the mains supply.20170707_121220.jpg
 
I misread your first post, a four way extension should be wired using 1.25 flex (13A) or 1.5 flex (16A). If it is contained within trunking he maybe theoretically correct depending on the cable csa but personally I think he is pushing the boundaries a bit far.
 
I was chatting with a PAT tester who mentioned that he would fail 4-way extensions where the flex had been trunked and the client was using them with appliances drawing 13 amps. His reasoning was that the trunked flex should be de-rated. Would you agree with this?
This PATester bit simple is he? what idiot is running an extension lead in trunking, wait a sec has someone hard wired this 4 way extension?
 
By trunking I think he meant a plastic u-shaped channel with a snap-on lid. I assume a 13 amp plug would be in use and the "trunking" added to provide some extra protection to the 1.25 flex.
 
I was chatting with a PAT tester who mentioned that he would fail 4-way extensions where the flex had been trunked and the client was using them with appliances drawing 13 amps. His reasoning was that the trunked flex should be de-rated. Would you agree with this?
Might want to derate the OCPD in the plug top, feeding the 4 way extension, if he is that much of a Jobsworth.
 
I have seen this but it isn't that common and I wouldn't worry too much as long as the correct fuse is fitted at the plug top. Extension leads in offices are rarely going to achieve their maximum rating.
 

Reply to 4-way extension with trunked flex in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

I am looking for advice on getting an upgraded 25 meter extension cable from my office into my car park to charge my EV from an IP66 rated socket...
Replies
7
Views
1K
Hi all, Disclaimer: I'm not an electrician and have very basic knowledge of electrical installation. We've been putting in a new kitchen into an...
Replies
17
Views
2K
Hi all, Was speaking to a family member recently, he told me his iron recently made a bang and flash as he plugged it in to the socket, and could...
Replies
14
Views
1K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
So I just started out recently and I’m struggling with what to price myself at. It’s worth noting I live in the east London area and I’m looking...
Replies
12
Views
525

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock