Looking at quoting to install said radial for kitchen appliances.

Can anyone say if they've ever fitted the Click Min Grid modules with 4mm looped into each switch. Click tech say max 3x2.5 or 1x6mm, but want to hear real world advice or experiences
 
I think you'd be hard pushed getting two 4mm² conductors into a termination of a grid switch.
Can't say as I remember working on any Click ones, but I have worked with MK and Crabtree ones.
 
but want to hear real world advice or experiences

Ditch the 4mm idea and stick to a ring
4mm radial to grid switches {filename} | ElectriciansForums.net
 
agree with above, but why not buy 1 switch and see if you can get 2 x 4mm in without snipping strands.
 
Running a ring to a single position for a 6 way grid, then out via DP switches, is this seen as 6 spurs from 1 point, or a spur from each DP switch?
 
If you loop in and out of each switch and then continue the ring from the last switch, it would be a spur from each switch.
 
so a single spur from each point, and so compliant?
 
Thankyou very much people. Had in my mind that it would be classed as 1 point, as in the grid plate. But fair enough, after reading your posts I now see clearer:conehead:
 

Reply to 4mm radial to grid switches in the Electrical Tools and Products area at ElectriciansForums.net

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock