  1. BristolSpark
    Offline

    BristolSpark Guest

    Hi

    We have to install a 63A supply to a new consumer unit on a 2nd floor studio flat. The supply at present looks like it may have to feed from the switch on ground floor outside the property and up the wall before re-entering the 2nd floor studio flat.

    Any thoughts how best to go about this.

    SAW cable or trunking with 2 core and seprate earth. some advise and thoughts on this would be good.

    Cheers
     
  2. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    SWA for me.
     
  3. BristolSpark
    Offline

    BristolSpark Guest

    We were thinking 16mm 2 core SWA, use the armoured for cpc, clip it all up the side of the building.

    The only thing is what about the standard consumer units, they not really designed for swa as they are plastic. Any thoughts on termination into the D/B.
     
  4. Dan23584
    Offline

    Dan23584 Electrician's Arms

    Location:
    Bristol
    Trunking will probably look better but it will be much more cost effective to go with SWA. I would choose the latter.
     
  5. JamesBrownLive
    Offline

    JamesBrownLive Guest

    What about installing one of these flush next to the CU, right where the CU entry cutouts are:

    http://www.******************/Products/BX333.html

    You can then terminate the swa into this and then run the cores up and through into the CU.
     
  6. JamesBrownLive
    Offline

    JamesBrownLive Guest

    OK, just go to T L C and do a search for BX 333.
     
    • Like Like x 1
  7. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    make sure the |SWA is switch/fuse protected, and a good 16mm fly lead from the gland at the CU.
     
  8. BristolSpark
    Offline

    BristolSpark Guest

    The client said the previous electrician on a different flat used the exisiting supply and just installed new consumer unit. But the cable looks like a 10mm rather than 16mm.

    Also is there any restriction on the height of the consumer unit. ie.....may have to install board around 500mm off the floor. Cant see anything in the on-site guide.
     
  9. Engineer54
    Offline

    Engineer54 Guest

    How are you going to be able to support the single cores in the trunking with strain relieve?? You can't just have them hanging in the trunking!! I'd Use 3 core SWA cable, as my first choice too...
     
  10. BristolSpark
    Offline

    BristolSpark Guest

    I agree the SWA sounds a far better option. I just to find a way to terminate it into a consumer unit. hey guys thanks for the advise.
     
  11. Engineer54
    Offline

    Engineer54 Guest

    A steel adaptable box springs to mind!! lol
     
  12. BristolSpark
    Offline

    BristolSpark Guest

    Yes sounds ok, but presentation will look awful. This D/B is gonna be on view lol...with a metal box in your face lol. need to find another way....
     
  13. santidreamer
    Offline

    santidreamer Guest

  14. santidreamer
    Offline

    santidreamer Guest

    Hmm blocked from posting links wonder why?

    go to screw fix and look for IP66 66 gland Kit 20mm

    63 Amps seem high for a small apartment is there a big power shower or hot air heaters?
     
  15. needasparks
    Offline

    needasparks Electrician's Arms

    Location:
    Essex
    Why does the armour need to be used at the cu as it will be earthed at switch fuse and it would be a 3 core.
     
Loading...
Similar Threads - supply required flat Forum Date
Domestic SWA free to outside pond - supply loss aren't required Electrical Forum Mar 22, 2016
Looped DNO supply? Any thoughts? Electrical Forum Jul 11, 2017
Running new cable to supply garage from sub-board Electrical Wiring, Theories and Regulations Jul 8, 2017
Seperate / Integral earth CPC on 400A supply Electrical Wiring, Theories and Regulations Jul 3, 2017
Unable to confirm Supply characteristics for hospital install Periodic Inspection Reporting & Certification Jun 29, 2017
2.5 spured of a cooker supply Electrical Appliances Forum Jun 27, 2017

Share This Page

  • Electricians Directory Post a Domestic Job Post a Commercial Job