Discuss 6mm2 for 8.5 kw shower in the Australia area at ElectriciansForums.net

Hi Flukey,
You may be right but the real problem is people walking into b&q seeing on a big board how to connect lighting circuits etc.They do not explain the regulations to these people,then when you try to do a proper install and then mention the price you always get funny looks !!! one guy recently called me in because his kitchen install was a complete balls up,said if i could first fix for him could he second fix to save money !!! Would he say that to a heating engineer - pipes are in, i will fit boiler - no.Most sparkys have spent years doing a good job unfortunatly some people still do not understand how skillfull you sometimes have to be,and knowledge we have to learn.Thats it moan over.!!
 
just to have me two pennies worth, i wouldnt even contemplate putting 8.5kw shower on a 6mm, the regs may not be statutory but when the **** hits the fan the court is gonna ask if it was done to current regs, your reply would be no sir, then its see ya later enjoy getting bent over in jail!

7.2kw is all i would put on a 6mm, be safe, keeo others safe and dont increase your chances of going to jail, is it really worth it???
 
HI SCOTT,
DEPENDING ON THE CONDITIONS THIS IS VERY POSSIBLE. I KNOW IT SOUNDS MAD NEEDING A 16mm TO RUN A SHOWER AND THE CONNECTIONS WILL BE A NIGHTMARE, BUT IF THE CALCULATIONS TELL YOU THAT IS THE CASE THEN SO BE IT. IN THIS CASE YOU HAVE TO LOOK AT YOUR INSTALLATION METHOD AND SEE IF RE ROUTING IS MORE PRACTICAL TO KEEP THE CABLE TO A SENSIBLE SIZE. ONCE AGAIN DO THE SUMS, REFER TO THE REGS AND YOU CANT GO WRONG ;)
 
Last edited:
I to work to current regs, have done my updated 17th course, registered with niceic as domestic installer, have all relevant insurances etc etc.

However i think a point has been missed here, you can put whatever shower you want on a 6mmt+e, just back it up with a 32a mcb, then when it surpasses this amount it will take the breaker out, cable safe.

The real issue is whether or not we want to do the job properly or not. for those that do don't bother arguing with those that don't. They are not going to change their minds and all they will do is hoover up the work we refuse to do.

I sometimes wonder who the real fools are!!!!!!
 
Thats a very relevant opinion.
Not sure i would want to keep getting calls from a customer though when their breaker keeps tripping when i could have installed the job correctly in the first place. :eek:
If my workload gets that low that i need to consider competing with sparks that use inferior equipment then i will review my policy at that time.;)
Until that day arrives i for one will carry on installing every job under the scope of the regs as they are intended :)
 
When installing any cables now make sure you stay clear of insulation.If needed suspend cables in loft on cable tray then drop down,yes ridicilous but have you ever been in a loft in the middle of summer ????
The regs are there to make sure of a proper installation - simple !!
Yes they are over the top, as i said before but the more regs the better as hopefully it will stop the cowboy sparks !!!

Hi, on what kfordhunter said - think ! when would the 32amp mcb trip on overload ??
Look at the time/current tables - you may be surprised !!! to see how much it could take therefore the cable is as well !!
 
Last edited by a moderator:
Hi Guys,
Read all the comments,where as i do feel that bs7671 does go over the top, i have just spent £280 on 17th edition course £100 on books,£450 to renew nic.I will stick to the regs as i have to and anyone else doing electrical instrallation work should do so as well.Its the only way to try to get standards up.It amazes me that for a few pounds more people compromise safety.Why is it our industry allows this i thought part p would sort it out,but it has not !!!
Compulsory “safety” does not come from cable size, however, it does come by adding an additional safety (in this case absolutely compulsory) called Residual Current Device!

When installing any cables now make sure you stay clear of insulation.If needed suspend cables in loft on cable tray then drop down,yes ridicilous but have you ever been in a loft in the middle of summer ????
The regs are there to make sure of a proper installation - simple !!
Yes they are over the top, as i said before but the more regs the better as hopefully it will stop the cowboy sparks !!!

Hi, on what kfordhunter said - think ! when would the 32amp mcb trip on overload ??
Look at the time/current tables - you may be surprised !!! to see how much it could take therefore the cable is as well !!
 
Last edited by a moderator:
simopesh,
i think you are missing the point here.
6mm doesnt meet the requirements of bs7671 which we all work to.
why would you want to install 6mm when you can install the correct 10mm and charge the correct amount for the job too.
the fact that the customer is old and has new tiles has no bearing on us as electricians to feel that because she doesnt want the decor damaged we must bend the rules.
you are quite right in saying that your way will work and i dont dispute that but what will your defence be if it did all go wrong??
as i said each to their own but i feel by keeping to the regs i will always have a clear conscience should the unthinkable happen
I do know what I’m talking about. Float of electrons and multi-core cable are laws of physics that I can talk on a much higher level.
What will happen if you install a shower with 10.0mm cable with loose connections? I’m absolutely shore that you know the answer.
In accordance with the current 17th edition the supply tails from meter to board are bound to be 25.0mm double isolated tales. Ok, but how does EDF or the rest of the suppliers comply with the above? Well, I’m afraid to say but they don’t. Some of the domestic households are with 10.0mm main supply piro cable with 4-6 storage heaters, immersion heaters (Low and Normal), electric cocker shower and more. Did you ever ask yourself how do the mains last when people override the tele-switch and everything is pushed to its limits? Believe me it does last!
I know by pure calculations that cable current capacity is largely downgraded for safety; however, with the current technologies its safety issues are unnecessarily exaggerated!
Regards
 
simopesh
i think we have all agreed that some of us work within the regs and some work without.
what you do is personal preference and the facts are in this thread for all to see and make their own minds up.
if it complies i do it, if it doesnt comply i dont. but thats my opinion and i am very happy with it.
i think this thread has lasted long enough now for everyone to decide which side of the regs they work to and i wish you all the best with your future install choices.:p
 
Sorry that I'm late in on this one. No, really I'm sorry I missed it. Been away from pc. I think it's obvious that there are some who will follow the regs and some who wont. Regarding cable sizing I would err on the side of caution but if someone else doesn't want to I can't make them, and if it goes tit5 up then they only have themselves to blame
 
Cant believe all the drama..i would have the install done in an hour rather than spending time worrying about it on here! im with flukey comply with regs..thers only one way n thats to do things right!! Regardles of what any little old lady says..remember its ur neck on the line and if the little old lady disagrees well let the cowboys in and leave with a clean consceince :)
 

Reply to 6mm2 for 8.5 kw shower in the Australia area at ElectriciansForums.net

Similar Threads

Hey all, Ive been in and out of a huge house rewiring as the renovate it for a year of so. Every is thing done and dusted except the downstairs...
Replies
3
Views
1K
Hi, I am changing the electric shower in a bathroom refurbishment (my own) and just wanted to ask about the mcb rating. The existing shower was...
Replies
2
Views
725
Hi, We are renting and have a electric shower downstairs (extension) - a 9.5kW Triton T80Z fast-fit electric shower as well as a combi boiler...
Replies
34
Views
4K
Hi My 4 bed 2 storey house was extended 2 years ago and completely re-wired, but I am having to upgrade the insulation and board out the loft...
Replies
0
Views
1K
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
159

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock