Discuss 7.4 - Suitability of enclosure(s) for IP and fire ratings (416.2; 421.1.6; 421.1.201) in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

Reaction score
116
Quick question. I have carried out a partial rewire, the client did not want a new consumer unit and so remains the plastic one. I noted on my EIC under comments on existing installation:

The existing consumer unit whilst in fair condition does not comply with regulation 421.1.201 if BS7671 :2008 AM3 2015 as it is not manufactured from non-combustible material.

However, on the schedule of inspections, item 7.4 - Suitability of enclosure(s) for IP and fire ratings (416.2; 421.1.6; 421.1.201), since we can only put a tick or N/A, I assume a tick does not mean it is ok, it just means it has been inspected. I.E. I tick it, I have inspected it and I have commented on it, all ok? OR..... by ticking it am I saying the enclosure is suitable?
 
Limitation of the schedules (if you excuse my pun!). You have inspected it, bought to the attention of the customer, and made a note in the comments.

Just because the existing CU is not compliant with current regulations (421.1.201) doesn't mean its unsafe or unusable. The only caveat, is if all circuits were rewired, and the existing CU was reused, I would suggest that goes against the suitability of existing equipment, reg 132.16, and therefore 421.1.201? What percentage of existing circuits remain? What does you scheme advise?
 
Limitation of the schedules (if you excuse my pun!). You have inspected it, bought to the attention of the customer, and made a note in the comments.

Just because the existing CU is not compliant with current regulations (421.1.201) doesn't mean its unsafe or unusable. The only caveat, is if all circuits were rewired, and the existing CU was reused, I would suggest that goes against the suitability of existing equipment, reg 132.16, and therefore 421.1.201? What percentage of existing circuits remain? What does you scheme advise?

I'll check with my scheme see what they think
 
Quick question. I have carried out a partial rewire, the client did not want a new consumer unit and so remains the plastic one. I noted on my EIC under comments on existing installation:

The existing consumer unit whilst in fair condition does not comply with regulation 421.1.201 if BS7671 :2008 AM3 2015 as it is not manufactured from non-combustible material.

However, on the schedule of inspections, item 7.4 - Suitability of enclosure(s) for IP and fire ratings (416.2; 421.1.6; 421.1.201), since we can only put a tick or N/A, I assume a tick does not mean it is ok, it just means it has been inspected. I.E. I tick it, I have inspected it and I have commented on it, all ok? OR..... by ticking it am I saying the enclosure is suitable?
I would mark it as N/A and write a note in the comments section
Just note that although it does not comply to regulation 421.1.201 it is installed to an earlier requirement of bs 7671 and has been verified as acceptable for continued use.
A bit like the Comments you have already made.
 
I would mark it as N/A and write a note in the comments section
Just note that although it does not comply to regulation 421.1.201 it is installed to an earlier requirement of bs 7671 and has been verified as acceptable for continued use.
A bit like the Comments you have already made.

Exactly what NAPIT have just said to me. Basically its N/A unless I installed it so he said you didn't install the consumer unit, the schedule of inspections is only related to the work I have installed.
 

Reply to 7.4 - Suitability of enclosure(s) for IP and fire ratings (416.2; 421.1.6; 421.1.201) in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

Similar Threads

Grateful for a kick in the right direction on the following: a telecomms engineer stated out that an outdoor metal cabinet (earthed & bonded) was...
Replies
22
Views
2K
I have been asked by Trading Standards to carry out a report on some electrical work installed by another company (5 years ago). The 'new' wet...
Replies
31
Views
3K
Hello everyone, I’m based in the ROI and live in a rural location. Yesterday evening my electricity supply started to switch on and off randomly...
Replies
2
Views
2K
Hi All, A top quality EICR report attached. I'm detecting an increase in opportunists looking to scare the bejesus out of landlords in...
Replies
43
Views
5K
  • Locked
Hello Guys I'm going to put my Tin hat on and close the curtains so the Regs police can't arrest me for asking this question again, I can only...
Replies
128
Views
53K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock