If I can manage to get my brain into gear,I think I will look for a logical regulation which frowns on such practices of using larger than life cable sizes on everyday accessories,extra naughty I believe :)
 
slightlyoff topic, but hre's something that has been bugging me for ages.

when applying the temp. factor ( 1.2 ) to your loop impedance as per osg., why apply it to the whole Zs value and not just to the R1+R2, when the supply cable from sub-station is never going to approach anything like 70 deg. ????

thoughts???
 
slightlyoff topic, but hre's something that has been bugging me for ages.

when applying the temp. factor ( 1.2 ) to your loop impedance as per osg., why apply it to the whole Zs value and not just to the R1+R2, when the supply cable from sub-station is never going to approach anything like 70 deg. ????

thoughts???
May be a good idea to add to the 18th consultancy debate Tel, but never given that much thought to it, make you think though, good point
 
slightlyoff topic, but hre's something that has been bugging me for ages.

when applying the temp. factor ( 1.2 ) to your loop impedance as per osg., why apply it to the whole Zs value and not just to the R1+R2, when the supply cable from sub-station is never going to approach anything like 70 deg. ????

thoughts???

Because it's a rule of thumb from the OSG.

You can calculate actual operating temperatures if you wish, and derate using those values. However I don't believe this would be worthwhile in a domestic environment.
 
slightlyoff topic, but hre's something that has been bugging me for ages.

when applying the temp. factor ( 1.2 ) to your loop impedance as per osg., why apply it to the whole Zs value and not just to the R1+R2, when the supply cable from sub-station is never going to approach anything like 70 deg. ????

thoughts???
We do by doing the rule of thumb 80% values of those given in bs 7671.
This has already been taken into account
As there's a 20% difference in operating temperature between 20 degrees and 70 degrees
Example if we want to adjust our zs value of 1.37 say 10 degrees for a type B mcb then it's 1.37 x 0.96=1.31
If we want to adjust back to 70 degrees then it's 1.31/ 1.2= 1.09 ohms which is our rule of thumb value.
 
slightlyoff topic, but hre's something that has been bugging me for ages.

when applying the temp. factor ( 1.2 ) to your loop impedance as per osg., why apply it to the whole Zs value and not just to the R1+R2, when the supply cable from sub-station is never going to approach anything like 70 deg. ????

thoughts???
May be a good idea to add to the 18th consultancy debate Tel, but never given that much thought to it, make you think though, good point
 
Tel said when the supply cable from sub-station is never going to approach anything like 70 deg. ????

A few years ago a new build hotel I worked on had 3ph 185 mm at the supply
A Jcb driver managed to chop the suppliers incomer
What looked like no bigger than about a 16mm suppliers cable for the hotel was also supplying a lot of the houses in the local area,I would think that cable was one hot cookie when in full flow
 
slightlyoff topic, but hre's something that has been bugging me for ages.

when applying the temp. factor ( 1.2 ) to your loop impedance as per osg., why apply it to the whole Zs value and not just to the R1+R2, when the supply cable from sub-station is never going to approach anything like 70 deg. ????

thoughts???

Which page of the OSG is the calc on?

At a guess they're trying to aire on the side of caution???. The actual design formula is Zs=Ze+1.2(R1+R2).

Problem is you get two different results. I've just plucked some numbers out of the air, Ze-0.35, R1+R2-1.12.

Using the design calc I get 1.274 ohms. Zs=Ze+1.2(R1+R2)

Using the OSG calc I get 1.344 ohms. Zs=1.2(Ze+(R1+R2))

So in some cases the incorrect CSA cable could be used, although this would only mean going up a size.
 

Reply to 8.5kw shower wires in 4mm, burnt terminals in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I have just been called out to another burning shower switch.Upon removal the wires had been burnt and chared.One thing I've noticed on all burnt...
Replies
27
Views
1K
Hi all, A few months ago we had a Triton Martinique 8.5kw shower installed. We've noticed that the temperature seemed quite low. Its what I'd...
Replies
13
Views
1K
Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me...
Replies
4
Views
382
At a bread and butter job, loose socket, socket not working, change two lights. Sticking out rather like a sore thumb was this (I removed the wire...
Replies
5
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock