Discuss Am2 in the UK Electrical Forum area at ElectriciansForums.net

S

Sparky92

Hi everyone,

Im going to be doing my am2 in September, I'm very confident with the build. The only thing I can't get around is the live tests, what order do the live tests go in? Also some help on fault finding.


Cheers

jimi
 
the tests are listed in the on-site guide along with pictures. However, you should be familiar with testing as it was part of the 2330 level 3, in which you were also required to build an installation and test it.

Anyways, dead tests first,

1. Continuity of protective conductors (two methods).
2. Continuity of Ring Finals (3 steps).
3. Insulation resistance
4. Continuity of bonding conductors
5. Ze
6. PSCC/ PFC
7. Zs
8. RCD times
9. Function Tests.

And I just wrote that off the top of my head after 3 pints. And I could do well before my AM2.

It's all there in the books my young fellow. Why not ask the foreman to be put on a bit of testing before as it's one of those things where practice really does help.

Also. with fault finding, there are only a few things that can be wrong e.g. Fault of negligible impedance (short circuit L/E, L/N), Open circuit, etc.. They simulate faults that you can find and identify with a simple multi meter. All you have to do is describe the fault, the likely cause and how you would potentially rectify it.
4. Ze
 
the tests are listed in the on-site guide along with pictures. However, you should be familiar with testing as it was part of the 2330 level 3, in which you were also required to build an installation and test it.

Anyways, dead tests first,

1. Continuity of protective conductors (two methods).
2. Continuity of Ring Finals (3 steps).
3. Insulation resistance
4. Continuity of bonding conductors
5. Ze
6. PSCC/ PFC
7. Zs
8. RCD times
9. Function Tests.

And I just wrote that off the top of my head after 3 pints. And I could do well before my AM2.

It's all there in the books my young fellow. Why not ask the foreman to be put on a bit of testing before as it's one of those things where practice really does help.

Also. with fault finding, there are only a few things that can be wrong e.g. Fault of negligible impedance (short circuit L/E, L/N), Open circuit, etc.. They simulate faults that you can find and identify with a simple multi meter. All you have to do is describe the fault, the likely cause and how you would potentially rectify it.
4. Ze
you missed out polarity live mate..
 

Reply to Am2 in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all. I recently failed a section of my AM2E assessment. Passed 7/10 but failed on some silly things I'm confident of correcting second time...
Replies
1
Views
309
Finished my AM2 the other day, pretty confident with most of it except the testing. When I done my live polarity, Ze and PFC tests for some odd...
Replies
9
Views
2K
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
554
I got a TEXT message (i dont know them and i cant find out who they are from the phone number) "Hi speaking from Indeed Are you available to give...
Replies
15
Views
845
Hi everyone, I'm nearly on my AM2 test and really enjoy the industrial side of things so I thought I'd learn by asking. I recently came across...
Replies
1
Views
736

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock