Discuss Asbestos in old ceramic 3036 consumer unit ?? in the UK Electrical Forum area at ElectriciansForums.net

Soulsurfer

-
Arms
Reaction score
143
Hey all,

Friend and client who rents out a flat has some works to do on electrical installation there, problem I have is old / very old consumer unit likely MEM 4 prong ceramic 3036 type re-wireable fuses / carriers, and the asbestos rope / weave webbing in the casing of them, prob Chrysotile (white) but still an issue, no log as it's a domestic and privately owned property but it's rented out and still dangerous stuff and there will be one or a few people liable if and when the board is removed and replaced with AMD 3 unit soon as is likely as I think the original C/U is 40-50 years of age and the main bonding and supplementary bonding is not right too.

I have been on phone and awaiting call back from H & S inspectorate regards whether I need to quote in a company licensed to remove the asbestos containing parts and or seal up area, PPE needed, and or anything else. As manufacturer is saying every single time a fuse blows the arc hitting the asbestos wadding will loosen it somewhat and that's never good, two gents I know have in past 5 months died with Mesothelioma and it wasn't pretty at all. Plus my friend / client is also a lawyer ! self explanatory why I also want to get things right. Any advice welcomed
 
I doubt whether the removal of it would be licenced work, but certainly proper precautions should be taken and the offending materials double bagged in Asbestos-marked bags. When inspecting installations with these I generally include in the limitations that fuse carriers are not to be removed for inspection owing to the presence of perhaps damaged Asbestos.
 
Hey all, yes been in touch with locall HSE and online got download too but seems open to interpretation, one advisor says use shaving foam to seal the C/U then chop all cores above the fuse carriers and double bag it properly ! Hmmm either way I'll go through the documents again I think. Thanks guys.
 
Yeah cut the cables at top of fuses. Just wear a white suit and a good mask. As sparks we have probably all drilled through it before without knowing!
 
It may be worth checking how much tbe asbestos company will charge you for disposing of it as it may not be much more for them to remove the flash pads for you they will give you the wast ticket and you don't have to worry about exposing yourself to the asbestos
 
just drag it out and chuck it in the bin. it's less dangerous than that bloody fibreglass in attics that we have to work with every day.
 
I removed a few three phase fused isolator switches a while back, containing asbestos flash guards. We marked the cables, and cut outside of the enclosure, sprayed water inside just to dampen down any loose fibres, then removed from the wall. I had to wear a FFP3 face mask, and double bag in marked asbestos sacks and cable tie shut. The office has a dedicated asbestos skip where it was disposed off (I think local rubbish dumps also have asbestos skips), and had to complete a waste carriers notice for the transportation of asbestos (this was all pre-approved by our H&S officer). We had also undergone an asbestos awareness course before hand. Small amounts like we were removing were fine, as we didn't remove any fuses as to disturb the asbestos. Obviously with large amounts, an asbestos removal company would be recommended.
 

Reply to Asbestos in old ceramic 3036 consumer unit ?? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

hello all...whats the typical cost for a new consumer unit fitted and the old wired fuse box removed im in a semi detached house in...
Replies
2
Views
234
Hi! I know the basics on a modern consumer unit, but I'm not sure on this old panel here. Could you help me know what I'm looking at? Seeing two...
Replies
12
Views
2K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
Hi all, new to posting but been reading for years. I inherited a house from my grandmother who passed in 2021, I intend to renovate and rent out...
Replies
97
Views
10K
I was testing a consumer unit before upgrading to current standards. (Old re wireable fuses) when testing one of the ring mains continuity i found...
Replies
16
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock