Siam
Determine the minimum size of cpc for the circuit giving consideration to; Disconnection times Thermal Constraints?
Here is what I have worked out so far for the circuit -
Ib=p/(Ulx√3) = 12000/(400 x 1.732) = 17.32Amps
From Table B6 I selected a C20 which has a max Zs of 0.87 Ω
20>17.32
Cable Selection
CA=1.03 Cg=0.70
It=In/cacg= 20/1.03x0.70=27.74A
I selected a cable size of 〖4mm〗^2 with a current carrying capacity of 28A, this was found from table 4D1A from the on-site guide.
Reference method B in trunking/conduit
9.5x17.32x42/1000 = 6.91V mv/a/m x ib x L
Yes, the voltage drop does comply.
Any help would be greatly appreciated.