Cheers guys. I've just had a read of the relevant section of GN8 but it didn't offer any reasoning behind the 8.5 factor and the difference between a CPC and bonding conductor in terms of copper equivalency.

['

A CPC's size is based on the temperature rise in the time it takes the ocpd to operate when a particular fault current flow. So this is looking at the ability of the conductor to survive a high current for a short length of time.

Bonding is sized considering its ability to safely handle a sustained flow of current.

Also it's worth noting that the table you linked to above is incorrect and has been for many many years.
 
They are for situations where you need to know the copper equivalent CSA, this is not used for bonding.

For bonding you need equivalent conductance, this is a different physical property. A factor of 8.5 is generally accepted as being the ratio of conductance of copper versus steel. So for a 10mm copper bond you need 85mm steel.
Theres an echo in here .......
 
Gn8 also gives warning to using the armour as a combined cpc/protective conductor as with tncs diverted neutral currents can raise the temperature of the cable meaning a increased sized conductors maybe needed for your ccc.
It's up to the designer whether this may happen or not.
 
Gn8 also gives warning to using the armour as a combined cpc/protective conductor as with tncs diverted neutral currents can raise the temperature of the cable meaning a increased sized conductors maybe needed for your ccc.
It's up to the designer whether this may happen or not.
Or rather raise the temp of the armour I should say
 

Reply to Bit quick advice please in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi Everyone, Last year arranged for my mother's and my consumer units to be changed by the same electrician who is NICEIC registered. Both jobs...
Replies
20
Views
2K
I've been told I need to upgrade the main earth bonding to 16mm. The consumer unit is on the wall adjacent to the externally mounted incoming...
Replies
30
Views
4K
Some friends are setting up a metal workshop inside a shipping container, on site at a commercial building that rents out studios, workshop space...
Replies
9
Views
1K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K
Hi guys I was recently ask by a customer if/how his house could be supplied by his electric car. He wants to charge the car at night on low rate...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock