waitees

Hi all

Been racking my brains on bonding, got the niceic man coming round next week and want to make sure its right. There was nothing left of the main earth from a tns supply it was all rotten, so the house had no bonding !

I have used 16mm as the new main bonding and 10mm for the gas and water 600m away incoming, is this the correct size earthing?. The board is wylex 10 way 25mm tails.

Please help !:confused:
 
the old earth clamp is still there i have put a warning label on it, the main earth is going straight into the board, no met
 
Last edited by a moderator:
All the sizes are fine. Is it a 951 earth clamp on the lead sheath, if it's original I would note it on my test sheet that you have informed the DNO that it needs changing and get a job ref number from them that shows they are aware it needs changing and put that in my comments on existing install box.
 
Thanks for the comments they are a great help !

Am i right saying then that it is down to the suppliers to get the earth clamp changed, i have been to some installs where the electrician has used a earth clamp on the sheath that is also used for the water and gas, i guess thats not they are supposed to do ?

Shall i note it in the comments box, notfied clamp in need of updating.
 
It's their responsibility, they should sort it out for you, notify them that a Hepworth braided earth strap is required, write this down in the comments box along with the job ref number they give you. You'll need an old bill from the customer as they will ask a few security questions. 951 earth clamps should never be used on lead sheath cable, potential crushing and shorting etc :D
 
Last edited by a moderator:

Reply to Bonding Puzzled ! in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Morning All, Think I'm having a brain fart but I have a 70mm2 4 core SWA with a separate 35mm2 CPC. Earthing is TNS with main bonding...
Replies
5
Views
1K
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
2K
This is a question (or discussion probably) regarding selecting the main earthing conductor, and subsequently the main equipotential bonding...
Replies
26
Views
6K
Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
Replies
21
Views
3K
Hi all, just looking for guidance on how you would code a 2.5mm main earthing conductor on a property with 10mm line conductor. Basically on a...
Replies
2
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock