OP
Squid
Sheathing, damn spell check on the Mac + Sausage Fingers.......Sheaving???
Discuss Burnt Main Downstream Neutral in the UK Electrical Forum area at ElectriciansForums.net
Sheathing, damn spell check on the Mac + Sausage Fingers.......Sheaving???
I suppose we are now implicated by also knowing and share the guilt. Oh oh!"guilty knowledge"
Can you explain the last paragraph in greater detail? R1+R2 were fine but rubbish/null IR readings?????There are two immersion heaters in one insulated tank. The first is a Heatrae Centerbrand Superloy 800 and is 2.8kW @ 230V. The other is a Backer 2.7kW @ 230V.
The owner was told that evening and I disconnected one of the immersions. I then replaced the burnt neutral with a new tail and terminated it to one of the non-melted points as a temporary, safe fix. The EICR has amongst over 20 other observations, a C1 for this....obviously!
A replacement 7671-3 CU is going to be done. I'll also run the immersions on an indep circuit protected with a 20A breaker as will the oven.
No - the outer sheathing had melted and globbed down the conductor.
Yes - the R1-R2 were fine but rubbish / null IR readings which is a real head-scratcher and I'd welcome any sensible avenues of investigation.
/ null IR readings which is a real head-scratcher and I'd welcome any sensible avenues of investigation.
I'll also run the immersions on an indep circuit protected with a 20A breaker as will the oven.
.
To cover you behind send the customer a Danger Notice without delay. It looks too far gone to be cured by tightening the screw up. What do you mean by IR is open circuit (OC) ?, if it is how have you got satisfactory r1+r2 ? You have what is known as "guilty knowledge" of a potential fire risk. Ideally tell them it must be isolated and the C.U. replaced immediately, I realise that may not be practical, so send the Danger Notice and make it their problem not yours ! Sorry if I sound like an arse but where there's a blame, there's a claim !! .
There are two immersion heaters in one insulated tank. The first is a Heatrae Centerbrand Superloy 800 and is 2.8kW @ 230V. The other is a Backer 2.7kW @ 230V.
The owner was told that evening and I disconnected one of the immersions. I then replaced the burnt neutral with a new tail and terminated it to one of the non-melted points as a temporary, safe fix. The EICR has amongst over 20 other observations, a C1 for this....obviously!
A replacement 7671-3 CU is going to be done. I'll also run the immersions on an indep circuit protected with a 20A breaker as will the oven.
No - the outer sheathing had melted and globbed down the conductor.
Yes - the R1-R2 were fine but rubbish / null IR readings which is a real head-scratcher and I'd welcome any sensible avenues of investigation.
He's probably using 230 v because that is what we are taught to use from college and bs7671.Only the lower heater should be connected in a two immersion heater cylinder if no off-peak/E7 supply is available.
The upper heater is only there to be a boost element in an off-peak/E7 setup. It will do little to no work if it is switched on at the same time as the lower heater, the heat from the lower heater will quite quickly operate the thermostat of the upper heater and switch it off. Also with modern immersion heaters the lower element can operate the overheat trip of the upper element and switch it off permanently (until reset)
Why are you quoting the 230V power ratings? The public electricity supply in the U.K. is 240V, the mythical 230V only exists on paper and not in the real world. These immersion are will be operating at 3kW and using the lower power ratings will lead to you designing and installing a circuit with a small overload which is a dangerous situation.
What is a rubbish/null IR reading? All of the IR testers I have used have only ever had a numerical scale so I haven't a clue what those readings equate to.
....Maybe it's not 'the real world' but it is whAt it is.
Yes it was to harmonise if you read page 316 of bs 7671 it was agreed by CENELEC within Europe from as early as 1988.Maybe a harmonized EUROPE ... or What it WAS ...
(did we ever intend to comply -or just upped the + to 10%)
Politicians promises , (-sounds good-) !!!CENELEC within Europe from as early as 1988.
He's probably using 230 v because that is what we are taught to use from college and bs7671.
We are required to record the nominal voltage on our test certificates as 230 volts and not the measured value.
Also voltage drop calculations are based on 230 volts it's 3% of lighting etc based on 230 volts yes it takes the worst case scenario.
Maximum zs values calculations require it to be 230 x 0.95.
Where I do agree that most of the time the voltage is around 240-245 volts it's not the voltage we are told to use maybe common sense tells us different.
Maybe it's not 'the real world' but it is whAt it is.