    Have a fault where the ecomony 7 (or whatever it's called) overnight water heater element keeps causing heat damage to the fuse in the local fused switch.

    The element seems to be 15A rated so the first time I was called out I told the landlord it was too high for the 13A fused switch and needed to be replaced with a 3kW element.

    What puzzles me is that the day time element is exactly the same set up and has never had the same problem....anyone any suggestions why?

    I've tested both elements and resistance on each is around 18ohms. Both circuits are giving similar continuity readings making me think it's not a loose/high resistance connection issue. (The heat damage was only around the fuse and not at any of the connections within the fused switch which also backs this up).

    Is it possible that the night time voltage could be higher causing the element to draw a higher current?

    And could I just replace the fused switch with a isolator and rely on the 16A re-wireable fuse at the consumer unit (run in 2.5 single cables in PVC trunking).....or should I put my foot down and tell the landlord he definitely needs to downgrade the element to a 13A??

    Any advice much appreciated :)
     
  2. Ian1981
    Offline

    Ian1981 Electrician's Arms

    Location:
    North east
    The off peak element is used the most so over time it has caused thermal damage to the 13amp fused spur.
    I would change spur and fit a 20 amp double pole switch.
    The immersion heater is a fixed load so wouldn't be subject to overload protection however the cable supplying the circuit and the heat resistant flex connecting to the element would require fault protection.
    1.5 heat resistant flex off the top of my head is rated to 16amps so can handle a 3kw load 13amps at 230 volts no problem.
    If it's 2.5 installed in trunking protected by a bs 3036 fuse 15 amp then Iz x 0.725 = 17.4 amps so cable is protected tho as I said overload protection wouldn't be required.
     
    • Like Like x 2
    Last edited: Aug 11, 2017
  3. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    FCUs do break down regularly when running high loads. asIan suggests, fit a 20A D/P switch in place of FCU.
     
  4. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    Just out of interest - the fcu that fails vs the one that doesn't - are they the same make?
     
  5. Ian1981
    Offline

    Ian1981 Electrician's Arms

    Location:
    North east
    I'm guessing the on peak boost switch is hardly used and when it is it's on for a small amount of time say an hour or 2 so the 13amp fuse won't be subject to an extended amount of use unlike the off peak spur which maybe subject to 7 or 8hrs of use give or take when the stat reaches desired temperature.
     
    • Agree Agree x 2
  6. PEG
    Offline

    PEG Trusted Advisor

    Location:
    Manchester
    Hi bud,is the off peak supply,via a separate meter?
     
Loading...
Similar Threads - Burnt fuse immersion Forum Date
8.5kw shower wires in 4mm, burnt terminals Electrical Wiring, Theories and Regulations Aug 1, 2017
Burnt Main Downstream Neutral Electrical Forum Jul 22, 2017
Burnt out start capacitor on car ramp Auto Electrician Forum Apr 19, 2016
16mm tails with 100A fuse ??? Electrical Forum Wednesday at 4:59 PM
Does a fuse/circuit breaker blow easier when there is high load on the grid? Electrical Forum Aug 4, 2017
100amp Switch Fuse required or not required? Electrical Forum Jul 20, 2017

Share This Page

  • Electricians Directory Post a Domestic Job Post a Commercial Job