Discuss Cable downsizing - lighting circuit in the Australia area at ElectriciansForums.net

DNS1

-
Esteemed
Reaction score
771
Hi guys,Got a kitchen on the end of a downstairs radial. 6A MCB, all in 1.5mm.Adding 3 further points on the end of the circuit (main ceiling light + undercupboard lights). Can I downsize the cable to 1mm?Current capacity is still fine (method c).Excuse the stupid question, but I can't find the relevant reg.
 
Which relevant reg are you looking for, there isn't one concerning that you can't reduce the size of a cable CSA in the same circuit, but quite a few that advise you can throughout the regs, under certain conditions.
 
My view would be as long as the Iz => In=> Ib is ok then it would be ok.


Would it not be better to keep it with 1.5mm for the sake of a few meters of cable ?
 

Reply to Cable downsizing - lighting circuit in the Australia area at ElectriciansForums.net

Similar Threads

Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
588
Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K
I live in a warehouse condo, converted about 20 years ago. The building dates to about 1870 but with the conversion, all of the electrical was...
Replies
3
Views
479
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi all, I have a light in the under stairs cupboard which is controlled by a switch in the hall. The under stairs cupboard is being taken...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock