I'd never heard of cold shrink shanky, looks a good ideayeah it looks obvious they have through crimped it to double insulated.
they should have used heat/cold shrink
Discuss Cable size in the UK Electrical Forum area at ElectriciansForums.net
I'd never heard of cold shrink shanky, looks a good ideayeah it looks obvious they have through crimped it to double insulated.
they should have used heat/cold shrink
hellerman sleeves are cold shrink, its usually not adesive though and relies on compression to stay on but lasts longer and looks better than tape (adesive heatshrink is best through)I'd never heard of cold shrink shanky, looks a good idea
Why would they have ID'd two of the cables as silver right at the point where the SWA cores join onto the tails? its obviously covering over a through crimp on what looks like 2 different sized cables
i might be looking at this wrong but looking at amendment 2 i thought the reason a evcp should not be connected to a pme system was to prevent back feed from the battery if a fault occurred.
722.1
(ii) protection for safety when feeding back electricity from an electric vehicle into a private or public supply network
and says
722.312.2.1
for tn systems the final circuit supplying a charging point for electric vehicles shall not include a pen conductor
so would it not be easier to use 3 core swa, amour earthed at db but not at evcp and use a tt system for the charging point than trying to meet 722.411.4.1 (i) or (ii) or (iii)
Probably they are thinking on the lines of Archy's suggestion, if the buildings phases are reasonably balanced, exemption i)
Well I called the NICEIC today and they said do not put an earth rod in and just take the SWA out the building and make it part of the TN-C-S installation.
I explained everything in full and explained the proximity to the building etc and that the building it metal and so on.
They even emailed me to confirm as I asked them, they said its fine, they said that in reality its never ever going to be a problem.
and also the fact that its a steel building with the steel bonded, he said thats more than likely better than any rod you will put in.
so would it not be easier to use 3 core swa, amour earthed at db but not at evcp and use a tt system for the charging point than trying to meet 722.411.4.1 (i) or (ii) or (iii)
They said the three phase part for section (i) and also the fact that its a steel building with the steel bonded, he said thats more than likely better than any rod you will put in.
More than likely better? That's a very precise and technical response!
Once you've tested the effectiveness of the steel structure as an earth then you will be better informed about this. Then with test results to prove it you could make the informed decision that this is safe to do.
First off I would be looking at the formula in the annexe associated with exemption i), then clamping the individual tails to see how balanced the building actually is when it is normally loaded, and adding up any further loads from the DB to see if it is possible to severely unbalance it, this would be my starting point.
I hinted at this last night when I said "Archies suggestion is looking better by the minute"
He's adding a 60A single phase load to the system, so unless the system is 60A out of balance then the system will be thrown out of balance when the charger is in use.
Clamping it will only give a brief snapshot of the loading, a couple of weeks load study would really be needed to establish a proper idea of what the loading is like.