james king

hi in collage today we were doing cable sizes and i am stuk on one question can any one help.

the question is

the load is 50Kw
3phase
the total lengh is 50m
its ran in metal trunking with 1 other circuit
30 degrees room temp

what will be the cablke size required and what mcb should be used?

i have had a look and i think it should be 16mm 5core and 125A mcb but i think im mising some thing. any one help
 
It does, not being awkward but if you get the answer without knowing how you got there its is about as much use as a choclate teapot
 
could you talk me through it step by step? its only the 3rd Q i have done on them only trying to learn and get my head around it, maybe it was a fluke lol
 
50kw/415= Ib 121A (Design current)
In= 125A (mcb)
125/.80= 157A what your cable should carry
It, tabulated current says you should go with 95mm squared

volt drop= 0.48(mV/A/m) x 121(Ib) x 50(length)/1000=2.9V

thats what i get,maybe make some sence to you
 
cables size your reccomended to go with, i cud be a bit wrong, im only on level 2:)

page 123-124 on site guide.
 
Last edited:
Havent got regs with cable tables to hand but we installed a 50kw induction oven about a month ago and it was protected by 125a mccb .

The reason I asked about the load is because if you look at the cable tables for current / VDPM will see that it's different depending on the load.
 
i take the cable you used was not 95mm lol? yes i relaise that but the Q does not state it im sorry! it says the machine is a bio fuel machine!!!

did you install the mccb into the 3phase CU then run SWA from there to a isolation point and connect the flex up in the out going of the isolator? just wondering how much big loads work
 

Reply to cable sizes in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Happy New Year all. Quick question regarding cable sizing. I have a 25m run from DB to car charging unit. The 25m run will mean approx 8m is run...
Replies
5
Views
650
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
689
I am an enthusiastic retired engineer rebuilding a barn in France from scratch and am having problems sizing my incoming electrical cables. I have...
Replies
6
Views
2K
Thinking of getting a Runpotec XB300 cable dispenser, as my yellow framed tripod thing is unsatisfactory for all the usual reasons. You can...
Replies
8
Views
576
Hi All I would appreciate some help with a few questions here regarding cables sizing, I'm using the latest 18th edition, amendment 2. Q1...
Replies
0
Views
891

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock