remember voltage is 400V so can expect to get considerably more power and 3x that because there are 3 phases :)

You would also see if Vd was ok using Vd = Ib x Length x mV/A/M (value found from table 6D2) it turn out ok - well less than 5%

These lecturers always keep the really tough questions til last means they won'tbe stuck withnothing to do at the end of the lesson ;)

hope i've been some help and not made some stupid mistake somewhere.
 
Think your all wrong here . 50kw is 217.39 amps split over 3 phases , 72.46amps per phase. its oven resistive load. nearest breaker 80amp triple pole . instaled in trunking ref meth 4 , 3or more cables . requires 35 mm cables. rating 89amps. from quick look . night all. Michelle.
 
Think your all wrong here . 50kw is 217.39 amps split over 3 phases , 72.46amps per phase. its oven resistive load. nearest breaker 80amp triple pole . instaled in trunking ref meth 4 , 3or more cables . requires 35 mm cables. rating 89amps. from quick look . night all. Michelle.

I wouldn't bet my life on me :D but your 217A figure comes from using 230 volts! It is 3 phase so you should use 400V and root 3
 
so how would the lay out work? i take it its just ran out the CU

you have been a great help thank you very much


probs to an isolator then to the motor - remember there is an mcb for each phase and if it is a motor they won't be type Bs

you still not seeing that button lol
 
brain in gear (just)

50x1000 50000
1.73x400 692 = 72.25a ( no correction factors taken into account)

correct and then share between 3 phases.

Edit: on reflection think your 72A is Il (line current) as the formula is for total power! so factors and mcbs should be done on that figure oops!
 
Last edited by a moderator:
cheers mate


Hey - you found that button :D

Edit ; when you have time have a read of the OSG chapter 6 and Scadden is a brill book for the theory - believe there is a new edition out now as well - well worth buying to get you thru your exams.
 
Last edited by a moderator:
just logged on to the office pc and computer says---

50kw - 90.32 amps length 50m voltage drop 11.29a type d mcb didnt allow for correction factors


Good Night
 
Last edited by a moderator:
calculate the desing current w/1.732 x 400 and that will supply current per phase (is what i should of said) unless there is a pf involved
 
Last edited by a moderator:

Reply to cable sizes in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Happy New Year all. Quick question regarding cable sizing. I have a 25m run from DB to car charging unit. The 25m run will mean approx 8m is run...
Replies
5
Views
649
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
680
I am an enthusiastic retired engineer rebuilding a barn in France from scratch and am having problems sizing my incoming electrical cables. I have...
Replies
6
Views
2K
Thinking of getting a Runpotec XB300 cable dispenser, as my yellow framed tripod thing is unsatisfactory for all the usual reasons. You can...
Replies
8
Views
576
Hi All I would appreciate some help with a few questions here regarding cables sizing, I'm using the latest 18th edition, amendment 2. Q1...
Replies
0
Views
891

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock