Discuss cant find what im looking for! in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
22
Ihave a job to move a cu. The plan/easiest option is to extend the tails already in henly blocks up into the attic (its a bungalow) across and back down. Works out to be 7m run. can anyone point me in the right direction in the big yellow book where i can find the relevant information on max length and methods of protection.
thanks in advance.
Danny
 
Recommended max length is 3m. It's not in BS 7671 as it's specified by the DNO. I think that's the generally accepted limit, but you could always have a conversation with the DNO for the area and get their view on it.

A suitably rated switch fuse at the origin should suffice (100A switch fuse with an appropriate fuse), and of course suitably rated tails.
 
Although a better solution instead of tails might be a run of appropriately sized SWA from the switch fuse, depending of course on the installation methods.
 
Ihave a job to move a cu. The plan/easiest option is to extend the tails already in henly blocks up into the attic (its a bungalow) across and back down. Works out to be 7m run. can anyone point me in the right direction in the big yellow book where i can find the relevant information on max length and methods of protection.
thanks in advance.
Danny
If you do use tails I would make sure that they are in some kind of containment including in the loft.
 
Agree with Dave 16mm swa on a 80 amp switch fuse should be ample depending on your maximum demand .
Swa should have the armour bonded to earth and if possible can be buried in the wall.
 
You don't want to rcd the tails as if the rcd trips you'll lose all the power to the house.
As long as you don't chisel them into the wall your fine.
TT is a different story tho
no its tncs
So stay away from 25mm SWA then, use a different size. It must be one hell of a big bungalow to need a submain that big!
Who mentioned sub main? Its the main board woth a total load of 70 amps
 
no its tncs

Who mentioned sub main? Its the main board woth a total load of 70 amps
If your extending the tails and going into a switch fuse ( don't know if you are or not) then the extended tails/swa via the switch fuse would now become a sub main to your consumer unit
 

Reply to cant find what im looking for! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, this is a repost of the initial in diy as the only potential diy aspect is the prep ahead of a qualified person attending, this is hopefully...
Replies
2
Views
1K
Hi all, first post so go easy! This is for people who are looking for more info on the course and exams and is from my experience of doing the...
Replies
1
Views
3K
So I am a fully qualified spark with my own company, however I also have a few properties I rent out. One of my tenants asked if they can have an...
Replies
84
Views
10K
Basic question to see if what I wish to do is correct: Client wants to build (or is building) and outside room (roughly 8m by 4m) to be used as a...
Replies
1
Views
1K
Hi there. I'm building a house and need some help with the LED lighting design. Lots of experience wiring things, some experience using LEDs (did...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock