Discuss Ci - for cable calcs in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

E

ennaress

Also just revising: trying to apply a rating factor for insulation on a cable calc. Just in theory, it's not for an actual job.
The cable will be clipped direct to joists above ceiling and is covered in >100mm thermal insulation. I cannot find the correction factor for insulation. Advice please!
 
You generally do not need to apply a rating factor for insulation as you would determine the installation method and then find the appropriate current carrying capacity for the cable in the appropriate table (in this case it sound like twin and earth so table 4D5).
Then you can apply any other rating factors to the tabulated value.
 

Reply to Ci - for cable calcs in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, just wondering if I have a cable passing through "100mm insulation at 2 points", do I use the correction factor of 100mm at 0.78 or 200 at 0.63
Replies
0
Views
194
Hi All, Just looking for some advice: I'm in the process of updating an old cable calc spreadsheet that helps to spit out Zs and Voltage Drop...
Replies
8
Views
866
Hi All I wanted to ask a question about the reference method. Passing wiring through holes made at 0.2-0.4 of the joist span. The cables passes...
Replies
1
Views
1K
Hi there, I'm Currently doing my design calcs for my college project and doing the actual Zs calculation. Formula is Zs= Ze (or Zdb) + (R1+R2)...
Replies
1
Views
1K
I'm currently refurbishing a room and in the process adding some internal wall insulation. The wall has been stripped and my electrician has...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock