3 core Swa feeding ip rated plastic sockets outdoors.
He 3rd core of the Swa has been used as a cpc but the armour is not connected to earth; but has been made off with metal banjos. Would this warrant a C2 or C3? I'm assuming as the armour isn't extraneous a C3? ?
Thoughts please ...
 
If there is good earth continuity of the SWA at the furthest point of the circuit and all swa glands are tight then I would go for a no code , I would only code 3 it if I thought by adding an earth continuity lead would improve the earth continuity considerably or felt that the SWA glands could start to fail in the near future do to corrosion etc
 
what's to investigate?
He's already established it's not earthed.

If the supply end of the SWA is terminated into a metal enclosure which may well be connected to earth but not very well ,further investigation may be needed to ensure a decent connection, IMO but then I was always careful, to be sure, to be sure.
 
Not in the new colours in a three core , they are all phases.
The new convention that seems to have been adopted is to over sleeve the black for the earth in single phase.
 

Reply to Code for Armour of Swa not being earthed... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
483
If cpc core is present i.e. it's either 5 core three phase or 3 core single phase — is a banjo connected with a brass screw into steel trunking...
Replies
7
Views
1K
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
677
I'm working on a system that has been installed incorrectly. It's a 3ph Hager board with 8 swa cables glanded into the bottom entry panel. The...
Replies
28
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock