Posting a message to the forum will remove the above advertisement

Discuss Code for lack of grommets/glands in Amd 3 Consumer Unit. in the Electrical Wiring, Theories and Regulations area at ElectrciansForums.co.uk.

Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. South Spark
    Offline

    South Spark Regular EF Member

    Location:
    South East
    As it says - what code should I be giving to a metal CU where the cables come straight in through the knockouts without any form of protection. Meter tails and main earth enter through different apertures 'n all.
     
    • Like Like x 1
  2. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    C2 in my book. no cable restraint and chance of shorting out to CU casing. potential dangerous. the different holes i'd code as C3 as the small eddy currents on a dom. will not cause a problem
     
    • Agree Agree x 1
  3. Ian1981
    Offline

    Ian1981 Electrician's Arms

    Location:
    North east
    Are the tails insulated and sheathed?
    Is there any signs of damage /abrasions to the tails?
    And is it TT?
     
  4. westward10
    Online

    westward10 Please don't bore me with your life story. Electrician's Arms

    Location:
    Northamptonshire
    You sure you should be doing EICRs.
     
    • Like Like x 1
    • Dislike Dislike x 1
  5. Risteard
    Online

    Risteard Electrician's Arms

    Location:
    Derry, Ireland
    Business Name:
    Walsh Electrical Services
    Whilst I agree that in reality it's unlikely to pose any real issue in a domestic installation I would still C2 it as it is not something which I would condone.
     
    • Agree Agree x 1
  6. Ian1981
    Offline

    Ian1981 Electrician's Arms

    Location:
    North east
    C
    C2 potentially dangerous?
    If there was evidence of thermal effects on the enclosure then that's the only time I would C2 it for tails entering different holes.
    Just my opinion tho.
    I'd be more concerned with the lack of protection to the cables entering the enclosure.
     
  7. Murdoch
    Offline

    Murdoch Electrician's Arms

    Location:
    Woking
    Is the main earth a"tail" ?
     
    • Agree Agree x 1
  8. Risteard
    Online

    Risteard Electrician's Arms

    Location:
    Derry, Ireland
    Business Name:
    Walsh Electrical Services
    It does have the potential to be dangerous, although as stated with the loads in a domestic installation this is unlikely.
     
  9. Risteard
    Online

    Risteard Electrician's Arms

    Location:
    Derry, Ireland
    Business Name:
    Walsh Electrical Services
    The earthing conductor must pass through the ferromagnetic enclosure together with the live tails. I'm not sure if that was what you were asking though.
     
  10. solarsavings
    Offline

    solarsavings Electrician's Arms

    Location:
    Cambridgeshire
    I think this one is c1.
    Done 3 months ago.
    No paperwork.

    Den 1.jpg

    Den 2.jpg

    Den 3.jpg
     
    • Disagree Disagree x 1
  11. Ian1981
    Offline

    Ian1981 Electrician's Arms

    Location:
    North east
    Yet a seperate cpc can enter a separate hole if ran in parallel with a swa
     
  12. Ian1981
    Offline

    Ian1981 Electrician's Arms

    Location:
    North east
  13. solarsavings
    Offline

    solarsavings Electrician's Arms

    Location:
    Cambridgeshire
    Went there today following a report of downstairs not working. She paid him £350 cash
    for that.
     
  14. Ian1981
    Offline

    Ian1981 Electrician's Arms

    Location:
    North east
    There's no eddy current issue for me
    Oh wait those photos are a different job unrelated
     
  15. South Spark
    Offline

    South Spark Regular EF Member

    Location:
    South East
    TN S. No signs of damage. I'm not doing an EICR just installing outdoor lighting.
     
Loading...
Similar Threads - Code lack grommets Forum Date
Crabtree c50 code 2 or not Periodic Inspection Reporting & Certification Jul 13, 2017
Code on eicr? help resolve an arguement Periodic Inspection Reporting & Certification Jul 12, 2017
EICR code Split cpc on ring final circuit Electrical Wiring, Theories and Regulations Jun 29, 2017
Code cables in walls with metal partitions Electrical Wiring, Theories and Regulations Jun 28, 2017
EICR codes .... AGAIN! Electrical Forum May 23, 2017
Communal Area EICR code Electrical Forum May 17, 2017

Share This Page

  • Electricians Directory Post a Domestic Job Post a Commercial Job