Coding for a 100mA RCD covering lighting circuit on a TT system in a domestic environment?
(Sockets on a 30mA, Ze of less then 50 ohms) (test data left in office along with books, just mulling it over during dinner)
 
None also can only Code on the lack of additional rcd protection for cables in walls, assuming they don't have earthed containment.
 
It would depend on if the lighting circuit supplies the bathroom light and if supplementary bonding was up to scratch for the bathroom imo.

circuit supplies bathroom, supplementary up to scratch-no code

circuit supplies bathroom, supplementary not up to scratch-C2

C3-due to lack of additional protection of cables buried in wall <50mm, not mechanically protected sufficient enough to stop the penetration of nails ,screws and the likes of or earthed metallic sheath/containment that meets the requirements of a CPC.
 
None,but you could C3 it. A comment in the comments box to cover your reasoning maybe
I presume he is referring to the buried cables?

If 30mA RCD protection is required now then not coding it is not an option. (This is specifically stated.)
 
Agree with all
No additional protection for cables buried less than 50mm in wall
No additional protection for circuits within a room containing a bath or shower
Both code 3 .
 
Thanks, thats what I thought - although there was something swimming in my head that all TT had to have 30mA in domestic for all circuits now (another C3 for that if so)

Also yeah, good Ra, in this area if the TT system is on the oxford or kimmeridge clay deposit soils we tend to get really good readings on TT systems
 

Reply to coding? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Good Morning all , Carrying out an EICR yesterday on a domestic property TT system , which is not a system I frequently work on. My question is...
Replies
21
Views
4K
Hi everyone I asked my assessor about touch voltage and he was not keen on explaining properly and gave me a rough answer which made me think...
Replies
32
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock