OP
amberleaf
( MEIWC)
Description of ( MWs)
The minor work mustbe so described that the work that is the subject of the Certificate . can bereadily identified .
120.3. & 133.5.
No departures areto be expected except in most . unusual circumstances . 633.1.
Installationdetails .
Method of faultprotection must be clearly identified .Automatic disconnection of supply . ADS
If the existinginstallation lacks either an effective means of earthing or adequate . mainequipotential bonding conductors . this must be clearly stated in the spaceprovided – 633.2.
Recorded departures. form BS-7671 . may constitute . non-compliance with the . Electricity Safety. Quality & Continuity Regulations – 2002 . as amended . or the Electricity at Work Regulations 1989 . it is important that the Client isadvised immediately in Writing .
Essential Tests .
Relevant provisionsof part 6 . Inspection & Testing –BS-7671 . must be applied in full to all ( MWs )
Where asocket-outlet is added to an existing circuit . it is necessary to :
i) establish that the earthing contact of thesocket-outlet is connected to the ( MET)
ii) measure the ( IR ) of the circuit that has been added to . &establish that it complies with Table 61 .
iii) measure the EarthFault Loop Impedance . to establish that themaximum permitted disconnection time is [Not Exceeded ]
iv) Check that the polarity of the socket-outletis correct .
v) if the work is protected by an . RCD . verifythe effectiveness of the ., RCD .
Description of ( MWs)
The minor work mustbe so described that the work that is the subject of the Certificate . can bereadily identified .
120.3. & 133.5.
No departures areto be expected except in most . unusual circumstances . 633.1.
Installationdetails .
Method of faultprotection must be clearly identified .Automatic disconnection of supply . ADS
If the existinginstallation lacks either an effective means of earthing or adequate . mainequipotential bonding conductors . this must be clearly stated in the spaceprovided – 633.2.
Recorded departures. form BS-7671 . may constitute . non-compliance with the . Electricity Safety. Quality & Continuity Regulations – 2002 . as amended . or the Electricity at Work Regulations 1989 . it is important that the Client isadvised immediately in Writing .
Essential Tests .
Relevant provisionsof part 6 . Inspection & Testing –BS-7671 . must be applied in full to all ( MWs )
Where asocket-outlet is added to an existing circuit . it is necessary to :
i) establish that the earthing contact of thesocket-outlet is connected to the ( MET)
ii) measure the ( IR ) of the circuit that has been added to . &establish that it complies with Table 61 .
iii) measure the EarthFault Loop Impedance . to establish that themaximum permitted disconnection time is [Not Exceeded ]
iv) Check that the polarity of the socket-outletis correct .
v) if the work is protected by an . RCD . verifythe effectiveness of the ., RCD .