Evening all.

Customer needs a new oven and electric hob. The current setup is 6mm T+E on 32A MCB, RCD protected, about 8M run, reference method 100. The oven they are looking at is 10.5KW. I initially thought that was too much but after adding diversity it seems ok. Are my calculations ok as I want to check.

My calculations are

10.5KW = 45.64A.

So 10A + 10.69A (30% of remainder f.l) with no socket = 20.69A

Think ive done everything right just seems 45A down to 20A is a big jump.

Does this sound ok.

Thanks in advance.
 
it`l be OK....remember that the oven will be massively overrated by the manufacturer....they tend to take the full load....rather than what will be on at any one time....so can the grill be on at the same time as the oven?

the cable is OK on a 32 A breaker....it should be fine...

if your really worried then connect up....clamp the cable...bet you get a surprise...
 
as glenn said. ^^^^. and i agree with your diversity calc. connect it up, get paid, onto next job. everyone's a winner.
 

Reply to Cooker circuit and diversity. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi folks, DIYer here, hoping for some advice before most likely calling in a spark. I'm looking to wire in new cooker and hob (separate units)...
Replies
1
Views
2K
I'd appreciate a quick sanity check, thanks in advance: New circuit for a 3 phase cooker, in a community centre (run by a charity). Total load...
Replies
2
Views
1K
Hi, I want to add a 32a induction hob and 13a oven to my cooker circuit. I was going to make the current single outlet dual and then upgrade the...
Replies
7
Views
5K
Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Replies
0
Views
3K
Hi all, Looking for some advice if possible please! Got one if then jobs that you get roped in to and that’s turned from a quick simple...
Replies
3
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock