Could someone please just giving me the nod that I'm not nuts!

Simple cooker swap big range induction beast with max draw of 16.2Kw

With a socket I make it 33Amp.

Imagine my confusion when customers shows me all the materials he has for the job which a spark has charged £500 for but no longer answers the phone. Big reel of 10mm swa, metal outdoor enclosures, industrial outdoor isolator, etc.

Dubious about this guys intentions!
 
Well the 10mm² is probably correct not sure about the cable run for the cooker unless it was previously on 6mm² and they were trying to get a new external cable route to the cooker?
I still cannot see where the isolator comes in surely you would want a cooker switch inside the kitchen.
 
I get if it was all new and needed replacing I'd install 10mm but there's a decent 6mm available.

Apparently he wanted to dig a trench then changed his mind and said he'd just run it through the loft with the old one. It's quite a long run maybe 15m but it's mostly clipped direct, no significant insulation.

I'm trying to give him the benefit of the doubt but me thinks he's just a chancer. I don't buy much industrial gear but I can't imagine 30m of cable and some switch gear coming to £500.
 
It was just a big empty metal box, 45amp (?) 1/4 turn switch, something in a contactum box. My only thought was maybe planning on a contactor outside kitchen with a switch inside but that's a lot of effort for a cooker!
 
No, cable had electricians delivery address on it

It's a rangemaster 110 don't have the model number at hand. I read their installation PDF and there wasn't anything specific just use correct cable and max size for terminals 100mm
 
Its never going to draw 16.2 KW.
For that make, I may be wrong, but not all ovens/grill can be on at the same time. As regards the hob, only one ring can have boost activated, if you boost another ring the other reverts back to its original power setting. Along with cycling and the unlikely case that all will be on at once (not a commercial kitchen). If you could swap the switch to one without a socket I'd bet you'd have no problems supplying this on a 32 Amp breaker. Dependant on length of run and install method the existing 6.00 will probably suffice.
Then again, as you have most of the gear you need to upgrade, then why not.
 
Last edited:
Thanks everyone, good point about swapping the cooker plate to remove socket. It's been running fine on a 32a MCB for a few days, just wanted to rest my mind.

I appreciate forgetting diversity, I suspect it wasn't an accident though. Same guy told another one of my customers they need a board change because a breaker kept tripping!

Also now I'm on a rant they say on their website they're registered with NIC & Elecsa
 
No, cable had electricians delivery address on it

It's a rangemaster 110 don't have the model number at hand. I read their installation PDF and there wasn't anything specific just use correct cable and max size for terminals 100mm

Right.... We have a range master 90 with a max wattage of 17.7 kw. The range master info for ours stated 6mm minimum
 

Reply to Cooker diversity calculations in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
425
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hi, I would appreciate some views on the following issue I have. The Cooker radial in a house has been wired in 2.5mm T&E, to save the expense...
Replies
12
Views
3K
J
Hi all, Looking at replacing kitchen. Current setup is 2.2kw oven, 5.6kw hob.. total = 7.8kw on 6mm cable, back to a 40a breaker. The current...
Replies
8
Views
10K
Sorry guys I'm sure these points have been raised before but been busy searching. I have been sent a diagram by the shop where we purchased our...
Replies
28
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock