midgetman

hi extended a 32 amp cooker circuit, adding a cooker switch and outlet plate. extended as it is a 7kw range cooker now situated in fireplace. old cooker now not going to be used.

problem is its on a 16th edition board and is on tt. the cooker and lighting are non rcd protected.

ideal would be to either go on rcbo or add another rcd.

how ever customer does not want to spend so can the cooker go on the 63amp rcd. there is no shower and only the rings on it.

as I said not ideal but got to be safer.

if above would then be notifiable and not minor works?

thanks
 
as I said not ideal but got to be safer.



thanks

But not safe! It is your name going on it, and you maybe doing him a favour saving him a few quid, but that will all be forgotten when someone gets hurt, and then guess where the finger will point.

Cheers...............Howard
 
cooker is on 32 amp mcb.
560d8599787ffb677fdd9dbfdf53e38d.jpg
 
But not safe! It is your name going on it, and you maybe doing him a favour saving him a few quid, but that will all be forgotten when someone gets hurt, and then guess where the finger will point.

Cheers...............Howard

Not safe with no over current protection? jeez
 
hang on. the cooker does not, nor has ever , required RCD protection. if the cable feeding the cooker isolator is buried<2" deep in wall/s, then that cable may need RCD.
 
cable is surface mounted. (fixed to wall securely behind kitchen units) however I thought all tt had to be now rcd protected..
 
you fit RCDs to a TT system if the Ze is too high to give acceptable Zs readings. a decent TT system with sub 1 ohm Ze may well negate the need for a RCD.
 
I can't see it being unsafe by putting on to the rcd side. inconvenient in case of fault but not unsafe.

maybe I see if I can find rcbo.. cheers
 
no problem with doing that, midget. better safe than sorry.
 
Am I missing something here. There's a spare way on the rcd side of the board so either move cooker over or get an rcbo. Issue mwc for extending circuit get paid run away ;)
 

Reply to cooker tt no rcd in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening all, If a socket circuit is not RCD protected via an RCD/RCBO and there isn't the option of fitting an additional RCD enclosure or...
Replies
20
Views
6K
Hi all,looking for some pointers to an RCD problem, I work entirely on large poultry farms, I've only been in post a year, at some point before I...
Replies
6
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Afternoon - despite a recent 18th edition pass (all but one right!) I'm having a bit of a moment whilst planning some upcoming works at our site...
Replies
24
Views
5K
Hi everyone, firstly hope you all had a great New Year. Wanted to get everyone’s thoughts on best design for Zappy EV charging point install...
Replies
8
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock