Thanks all, marvo I'm also convinced the moisture is eminating from the gland entry point. As you say, the rust is only present by that particular gland. However, the CU is well over a metre from ground level!?

In regards the CU construction material, BG website isn't particularly helpful but a magnet isnt attracted so, as Richard suggests; likely to be Al or alloy.

When I get chance I'll strip it down and provide an update.

IMG_5676.JPG
 
What a lash up of an installation!

It looks like there is a bit of corrosion around the other two glands at the bottom, and if it is non-ferrous then I'd guess that there's a quantity of aluminium in the alloy which has led to galvanic corrosion.
 
The absence of earthing conductors to the other SWA glands would perhaps indicate that any voltage on the armour of those SWAs would cause a current through the shell of the CU and this would be directed to the incoming supply gland and would be consistent with the levels of corrosion in that the maximum current would be at the incoming earth and lesser current at the circuits passing through the CU.
 
Poor termination method, was the paint cleaned from the CU prior to Glanding, all very well using Piranha washers, preparation is everything, pity they don't teach that on the courses, isn't it?
 
No I mean isn't that tail isolated from the earth bar? I don't see any electrical connection between the enclosure and the earth bar
.
 
No I mean isn't that tail isolated from the earth bar? I don't see any electrical connection between the enclosure and the earth bar
.
that might be the problem. causing (possibly leakage) current to flow through the enclosure. clutching at straws here, just thinking aloud.
 
No I mean isn't that tail isolated from the earth bar? I don't see any electrical connection between the enclosure and the earth bar
.
The main earth is inappropriately connected to the mounting screw holding the earth bar retaining strip to the body of the CU, however there is a metal connecting plate from the mounting screw to the earth bar, you can just see it entering the left most earth terminal, so there is earth continuity between all points (except the armour of the incomer!)
 
What a lash up of an installation!

It looks like there is a bit of corrosion around the other two glands at the bottom, and if it is non-ferrous then I'd guess that there's a quantity of aluminium in the alloy which has led to galvanic corrosion.
It looks like the paint was cleaned off or maybe flaked away when the nuts were tightened, I can't see corrosion though.

Completely agree that whole enclosure is a dogs breakfast. Never ceases to amaze me that even with the right tools and decent materials you could end up with such a poor quality installation.
 
I got time last night (before Poldark) to swop out the gland and investigate the damage. As Marvo suggested, moisture has been entering the CU through the supply cable SWA; rain water appears to be entering the SWA via a degraded external joint box, this is then compounded by the use of a sealed outdoor gland which is preventing moisture escaping. The moisture ingress appears to have caused the steel locknut on the gland to corrode and expand resulting in mechanical failure of the gland body as it passes through the CU casing.

There is no evidence of corrosion to the CU casing or gland body. Provisional checks suggest water hasn't entered L N flex within the SWA, I need to do a full insulation test to establish this fully.

Westwood, I have replaced the CPDs with compatible Schneider type.

Richard, the other glands are future spare capacity - earth bonds will be provided when they are utilised.

DaveSparks - outrageous!

Marvo - jees, tell it how it is.

Thanks again
 
Richard, can you clarify what is inappropriate regards the earth connection.

The main earth is inappropriately connected to the mounting screw holding the earth bar retaining strip to the body of the CU, however there is a metal connecting plate from the mounting screw to the earth bar, you can just see it entering the left most earth terminal, so there is earth continuity between all points (except the armour of the incomer!)
 
Good to hear feedback about the fault, thank you.
Richard, can you clarify what is inappropriate regards the earth connection.
The fixing for the earth and neutral bar support is not intended for use as an earth connection for another cable and making changes to this connection could cause a loss of earth continuity to the body of the CU. The ring crimp that has been used appears to have been either closed down or cut down in order to fit into the space, which could limit the effectiveness of the connection.
In all likelihood the connection is fine but it just has the potential to cause problems and fitting it directly into the earth bar would reduce the risk.
 
Following comments regards MCB compatibility and earth terminations, Schneider CPDs have been replaced with BG ones - the incoming isolator and earth was over complicating matters so these have been removed.

Ben-Curry.jpg

Picture courtesy: professional-electrician.com

God bless and sweet dreams.
 

Reply to Corroded swa gland - garage CU in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good Morning everyone. Quick question regarding a sub main from a TNCS supply feeding an outbuilding on TT. This is a domestic installation not...
Replies
7
Views
3K
Hi all, My first post here, thought I'd see if it was possible to get some advice or tips... Basically, I had a large amount of block paving and...
Replies
80
Views
12K
I would appreciate peoples thoughts on fixing this earthing setup to correctly separate PME & TT: Setup: Workshop at the bottom of a long garden...
Replies
31
Views
10K
Background: Served my apprenticeship 1964 to 1969 with NORWEB but not been directly employed in the industry since then. I have just laid a 10mm...
Replies
27
Views
9K
Hi. This is a gloriously messy installation I looked at this morning at a house a friend just purchased. It t became quickly clear it was more...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock