Hi guys.
After some confirmation from the majority about a few questions our recent assessor had in regards to our certification and some answered questions/suggestions;
Cert: In regards to supply characteristics and earthing arrangements. System was a TN-C-S, I was always taught that a TN-C-S system was a.c. 1 phase (2 wire) as the incoming cable would be a single line and combined neutral equalling 2 conductors (obviously split at head). I was told otherwise on the assessment and that a TN-C-S would be a.c. (3 wire) with TT being the only a.c. (2 wire) connection - any thoughts...?
Questions re RCD protection on condition report, I'd considered lack of on sockets to be a C3 but was told any downstairs socket could supply outdoor equipment so should be C2, surely any household socket could supply outdoor equipment with the use of an extension lead so should we be coding all non rcd protected sockets as C2?
Example of a C3 re: condition report. I went obvious lack of circuit details, lack of rcd protection on buried cables. I was then told to think more basic and that a cracked bayonet fitting on a ceiling would count on a high ceiling. Again any cracked fitting I'd personally be inclined to code a C2 or maybe C3 with a notice to consider replacing if no access to live parts however in regards to placing out of reach again I was taught that we couldn't use this method in a domestic setting (only in premises which are supervised by a skilled person).
Just after some reassurance for future purposes to make sure we're doing our job correctly.
All opinions appreciated.
Thanks, Joe.
After some confirmation from the majority about a few questions our recent assessor had in regards to our certification and some answered questions/suggestions;
Cert: In regards to supply characteristics and earthing arrangements. System was a TN-C-S, I was always taught that a TN-C-S system was a.c. 1 phase (2 wire) as the incoming cable would be a single line and combined neutral equalling 2 conductors (obviously split at head). I was told otherwise on the assessment and that a TN-C-S would be a.c. (3 wire) with TT being the only a.c. (2 wire) connection - any thoughts...?
Questions re RCD protection on condition report, I'd considered lack of on sockets to be a C3 but was told any downstairs socket could supply outdoor equipment so should be C2, surely any household socket could supply outdoor equipment with the use of an extension lead so should we be coding all non rcd protected sockets as C2?
Example of a C3 re: condition report. I went obvious lack of circuit details, lack of rcd protection on buried cables. I was then told to think more basic and that a cracked bayonet fitting on a ceiling would count on a high ceiling. Again any cracked fitting I'd personally be inclined to code a C2 or maybe C3 with a notice to consider replacing if no access to live parts however in regards to placing out of reach again I was taught that we couldn't use this method in a domestic setting (only in premises which are supervised by a skilled person).
Just after some reassurance for future purposes to make sure we're doing our job correctly.