Hello can any body help I have been pulling my hair out for 2 days in a carehome we have a ctec conventional panel that is coming up zone 6 fault the problem is its in fault sometimes for 2 seconds then clears sometimes 5 to 10 mins which is not giving me enough time to properly investigate. I have ruled out the panel by changing zone 6 for zone 5 and the fault moved to 5 I have been round every head and tightened connections. The EOL seems fine because I fit it in the panel and no fault. I thought I had sorted it as the last fault was 11.30 am then on my way home at 5 was phoned by home to say it had gone in fault for about 30 sec then cleared.
 
Intermitant faults can be a pain....and can be avoided if treat like any other cable on installation, with a full insulation test. Back to basics bring the eol cap forward in the zone circuit say half way. if fault clears start moving the eol cap back at each device until fault appears again. this will give you the location of the fault....suggest then carry out insulation test between the last device to prove cable.
 
Thanks but its the shortness of the fault that's confusing me as I said sometimes a sec sometimes 10 mins which gives little or no time to trace fault as soon as I get my tools out its cleared and was ok for 4 hours this afternoon
 
looking at the basics, it appears to be possibly a poor connection, maybe at one of the detectors.
 
Thanks but its the shortness of the fault that's confusing me as I said sometimes a sec sometimes 10 mins which gives little or no time to trace fault as soon as I get my tools out its cleared and was ok for 4 hours this afternoon

This is why you need to move the eol cap to prove devices. Only other way is to disconnect devices and proceed with an insulation test.
 

Reply to CTEC intermitant zone fault in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hi, I need to extend a fire alarm, the panel is a CTEC CFP 2 zone one and currently it has a couple of apollo alarm sense sounder bases/heads on...
Replies
38
Views
4K
I am interested in having a home generator that would provide power to my home when the power is out during hurricane season, etc. I have 2...
Replies
0
Views
260
Hi. Not sure if it's the right place to ask, so won't be upset if it gets removed. Apologies if the terminology (PEN/PME/etc) is used...
Replies
44
Views
6K
Hi all, I`m hoping someone can give advice how the following will work: I have 1 x C-Tec CFP 4 zone conventional panel i need to link to the...
Replies
6
Views
7K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock