@Lorzor I have deleted the images in your opening post for obvious reasons.
 
Looking at the service head on arrival I would have assumed a (slightly odd) TNCS arrangement.
The earthing conductor (even though in this case it is a gas bond) cable would not normally exit at that point, but no reason for it not to do so.
On measuring Zs at the consumer unit and getting a 0.11 ohm reading I would initially assume I was correct.
On attempting to measure Ze and checking the bonding arrangements I would then have been confused on finding the conductor from the service head was solely terminated onto the metal gas pipe.
On removing this conductor from the gas bond (and disconnecting the other bonding) I would then expect the Ze reading to be significantly higher since I would expect that the gas pipe was being used as the means of connecting the means of earthing to the installation (not permitted).

Because you have disconnected the bonding and got a Ze reading of 0.11 ohms there must be another means of earthing the installation, either the conductor from the service head is split in two at some point and goes off to the consumer unit and to the gas or there is another unseen conductor earthing the consumer unit.
If there are any other 6-16mm² green and yellow conductors in the consumer unit, that are not identified bonding, then I would be attempting to trace where they go and see if there is another reason for the low impedance.
 
Looking at the service head on arrival I would have assumed a (slightly odd) TNCS arrangement.
The earthing conductor (even though in this case it is a gas bond) cable would not normally exit at that point, but no reason for it not to do so.
On measuring Zs at the consumer unit and getting a 0.11 ohm reading I would initially assume I was correct.
On attempting to measure Ze and checking the bonding arrangements I would then have been confused on finding the conductor from the service head was solely terminated onto the metal gas pipe.
On removing this conductor from the gas bond (and disconnecting the other bonding) I would then expect the Ze reading to be significantly higher since I would expect that the gas pipe was being used as the means of connecting the means of earthing to the installation (not permitted).

Because you have disconnected the bonding and got a Ze reading of 0.11 ohms there must be another means of earthing the installation, either the conductor from the service head is split in two at some point and goes off to the consumer unit and to the gas or there is another unseen conductor earthing the consumer unit.
If there are any other 6-16mm² green and yellow conductors in the consumer unit, that are not identified bonding, then I would be attempting to trace where they go and see if there is another reason for the low impedance.

That was my guess, I'm going to attempt to find another method of earthing. It seems there may be quite a large cavity behind that service head, so it may be behind there. Don't worry, I won't dismantle it to get behind!
 
Is the house semi-detached or maybe terraced? I've been in a semi detached TT house with Ze (measured through the rod, main earth disconnected from CU) of 100ish ohms, but Ze measured at the CU with everything connected it was right down to 0.20 ish. Next door had been converted to PME and there was a metallic path between the properties, I think through the plumbing systems, boiler CPC etc. So even with the means of earthing disconnected in this house, it appeared that Ze was stil 0.20 ohms.
 

Reply to Difficult Service head in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, I'm shadowing the electrician who is doing our EICR's and after visually inspecting the service cable and service head, I noticed a bit...
Replies
12
Views
1K
I had a look at a property with this old service head. It's a looped supply, the met is just a bolt and the tn-s earth is questionable. There's...
Replies
13
Views
3K
I’m not working on this… not yet anyway, but can someone tell me why there’s a fuse or a link on the earth here? The green wire is bonded to...
Replies
3
Views
276
Evening Chaps As can be seen in the attached photo , the incoming supply cable has a Earth soldered to the outer sheath of the cable suggesting...
Replies
10
Views
1K
Hi there, I was wondering if anyone could advise me on the WT Henley Series 8 house service cutout. I have one of these installed at my house and...
Replies
3
Views
520

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock