Hi chaps,
Does anyone know if it is possible to use a daylight dimming sensor on a basic switch dim config or does it need to be DALI?
I've recently taken over a job from another spark, and the spec states to incorporate daylight sensing as well as manual dimming via a retractive switch into the circuit but the system has been wired with a dimming pair ie switch dim and fitted with Hager Klik boxes??
I thought it would need to have a control ie DALI??
Any help would be appreciated.
Regards
Mark