Saw an installation today where an upstairs consumer unit is run off a 40A MCB in the main board.
Two problems
1) Both boards are protected by 30 ma RCD so no discrimination.
2) There's a 40 A MCB in the second board as a dedicated shower feed - the installers have put a 10.8 kw shower on it and of course it keeps tripping the 40A breaker in the main board.
My question is - assuming the cable feeding the secondary consumer is adequate and I feed the upstairs board from on a separate mini consumer unit with a 60A breaker and 30 Ma RCD does that count as a new consumer unit for testing and certification purposes? i.e will I have to sign off on all the upstairs circuits?
Two problems
1) Both boards are protected by 30 ma RCD so no discrimination.
2) There's a 40 A MCB in the second board as a dedicated shower feed - the installers have put a 10.8 kw shower on it and of course it keeps tripping the 40A breaker in the main board.
My question is - assuming the cable feeding the secondary consumer is adequate and I feed the upstairs board from on a separate mini consumer unit with a 60A breaker and 30 Ma RCD does that count as a new consumer unit for testing and certification purposes? i.e will I have to sign off on all the upstairs circuits?