Discuss Do hand dryers require RCD protection in the Electrical Appliances Forum area at ElectriciansForums.net

C

C&H

Guys i'm doing an EICR at the minute. Do hand dryers for public use require RCD protection? Wired in singles in earthed steel pipe, no bath or shower in the room........
 
but on a EICR, the worst he can do is a code C3, or a comment recommending RCD protection.
 
If the hand dryer is hard wired on a TN system and as the cable is conduit run and is not in a room containing a bath or shower then the regulations do not require RCD protection of the accessory.

However probably a good idea anyway!.
 
Shouldnt be coded at all if it's not a requirement of 7671....this is why EICR's vary so much,electricians introduce personal opinions when the ONLY criterior is whether it complies onr not.
 
Guys i'm doing an EICR at the minute. Do hand dryers for public use require RCD protection? Wired in singles in earthed steel pipe, no bath or shower in the room........
Depends on the type of installation, I would avoid RCD protection on fixed equipment at all cost, however if TT for just one example then it would need it, whats the earthing arrangements and whats the zs reading?
 

Reply to Do hand dryers require RCD protection in the Electrical Appliances Forum area at ElectriciansForums.net

Similar Threads

Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
655
Hi all, Just a quick one regarding the need for RCD protection for socket outlets rated up to and including 32A. I have been tasked to install...
Replies
17
Views
1K
Afternoon everyone, I have a quick question about the Tesla Gen 3 Wall Charger? Does it require Type A 30MA RCD protection or not. Only because...
Replies
3
Views
1K
Hi there , Currently doing a college project where i need to select protective devices for the contract. I'm now at the point of selecting SPDs...
Replies
5
Views
2K
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
844

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock