I know that having a neon in the circuit screws up IR testing, but I just wondered if the same applies to Zs testing.

Many thanks

Whenever there's a low IR thread on here someone always pipes up 'is there a neon?'. But bear in mind it would only affect a L-N test, as would any other load connected. A neon will make no difference at all to IR tests to earth.
 
And resistance wise, I think the neons are 200k Ohms (ish), so even if they were in the circuit, they're not going to make an impact on a measurement that's 1 Ohm :)

I'm sorry Wilko, maybe I'm just being dense, which is more than likely :confused: but how would a resistance of 200k ohms not have an impact?

Cheers
 
I'm sorry Wilko, maybe I'm just being dense, which is more than likely :confused: but how would a resistance of 200k ohms not have an impact?

Cheers
Hi Joe - just imagining the earth fault loop impedance is expected to be about an Ohm (or so) and if somehow a neon was wired in error from L to E, then its 1 Ohm in parallel with 200,000 Ohms, which is 1 Ohm :)
 
Hi Joe - just imagining the earth fault loop impedance is expected to be about an Ohm (or so) and if somehow a neon was wired in error from L to E, then its 1 Ohm in parallel with 200,000 Ohms, which is 1 Ohm :)
your maths has had me flabbergasted and on 2nd thoughts my flabber has been gasted again. the answer is actually 0.999995 ohms. get it right. :D
 
Hi Joe - just imagining the earth fault loop impedance is expected to be about an Ohm (or so) and if somehow a neon was wired in error from L to E, then its 1 Ohm in parallel with 200,000 Ohms, which is 1 Ohm :)

Cheers, I was of course forgetting that the neon is in parallel not series. Time to go to Specsavers, my special glasses are obviously playing up :rolleyes:
 

Reply to Do neon indicators affect Zs test results? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
568
Hi all, Just a quick one, I want to use an ip rated light switch with a neon indicator to manually ovveride a PIR detector controlling an e27 LED...
Replies
1
Views
1K
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
621
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock