Discuss Do socket outlets in a Pub need to be RCD/RCBO protected! in the UK Electrical Forum area at ElectriciansForums.net

Normally I would say if inspected to BS7671 C3 however I see page 11 regarding installations to earlier editions "this does not mean that they will fail to achieve conformity with the relevant parts of the EWR 1989.Also regs 114 & 115.Having thought about it I am I & T to BS7671 so C3,C2 if it was a outside socket. The pub should have a risk assessment in place to the activities taking place on its premises.
 
Normally I would say if inspected to BS7671 C3 however I see page 11 regarding installations to earlier editions "this does not mean that they will fail to achieve conformity with the relevant parts of the EWR 1989.Also regs 114 & 115.Having thought about it I am I & T to BS7671 so C3,C2 if it was a outside socket. The pub should have a risk assessment in place to the activities taking place on its premises.
A statement suggests that an installation installed to an earlier Edition may not necessarily be unsafe. That certainly isn't the same thing as stating that it definitely is safe, however.

It is clear that since RCD protection is now required it must be attributed a coded observation. It is up to the Inspector to assess how serious the ommission of RCD protection is. So certainly it could be justified to suggest that C3 is insufficient in the particular circumstances, and that, therefore, a C2 would be more appropriate.
 

Reply to Do socket outlets in a Pub need to be RCD/RCBO protected! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Just a quick one regarding the need for RCD protection for socket outlets rated up to and including 32A. I have been tasked to install...
Replies
17
Views
1K
Hi, This post is about my concerns with medical IT socket outlets and want to alert you all if you are fitting them in a hospital. The current...
Replies
20
Views
2K
Hi there , Currently doing a college project where i need to select protective devices for the contract. I'm now at the point of selecting SPDs...
Replies
5
Views
2K
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
674
Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection. Was after a larger unit with...
Replies
65
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock