Discuss Do you need an earth rod for an outbuilding? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Hi Josh, I'm thinking this design may be affected by reg 434.2 and 434.2.1(i) which seems to limit length of an un-fused spur to 3m.
I would add a new radial to CU. Cheers.
 
So it seems, probably doesn't need a CU just fit socket/s straight to it with a FCU for the lights.
 
If the ring in the house isn't RCD protected then I'd make the FCU an RCD unit so that the SWA is RCD protected as so is the shed.

TFP10WL TIMEGUARD, CONNECTION UNIT, RCD, FUSED, WHITE | Farnell element14 - http://uk.farnell.com/timeguard/tfp10wl/connection-unit-rcd-fused-white/dp/1642925?

A small CU in the summer house with a 10A for the sockets and a 6A for lights would then be ok.

That then opens the question of: Should the shed CU be metal...?

If remote from the house and not part of the habitation then possibly no but as its wood its flammable.
 
And maybe 5 would understand why their doing it which way!

Yes big spark. You're 100% right.
The trouble is, all electricians give a very convincing argument for either method.
So it's finding out which half of the discussion, those 5 belong to.
Especially when this is this first time I have had to think through this particular issue.
I wasn't trying to insult anyone.
 
Josh Josh Josh i have looked at your thread and have joined to reply to how unhelpful and belittling the support some people give. but others are there to help.
 
I'm not sure .I've always put Rod in but saw an article and it said it could create problems

Welcome to the forum! Worth bearing in mind this thread is around 7 years old though.
 

Reply to Do you need an earth rod for an outbuilding? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
496
Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
Replies
8
Views
1K
hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
264

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock