Discuss Does a sunbed require RCD? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
38
Hi
I've been asked to install a power supply for a sun bed in a salon:
Sunbed is 60 x 225w lamps = 13.5K
Divide 230v = 59amps
Table 4D2A:
10mm T&E 63amp capacity clipped direct.
I'm installing a dedicated CU with a 63a MCB and isolator fed via a henley block on the meter tails for the sunbed to avoid the basement studio being plunged into darkness!
So far so good.
I haven't got paperwork for the sunbed but I understand that the ballasts typically have an earth leakage current of 75ma which increases over time. So 30ma RCDs can't be used. 100ma are not recommended for shock protection.

Am I required to protect this circuit with an RCD?

Thanks
Steve
 
IMO, an RCD is not required as long as the cable is not buried in a wall <50mm deep. however, i'd be measuring Ze and calculating Zs and PEFC to ensure that the cpc in 10mm T/E was adequate.
 
Thanks for the quick responses, much appreciated.
The manufacturer, Sunquest's (Aurora) website has very basic information unfortunately.
Client bought the most powerful model before taking advice on the power requirements of course. Luckily only a 3 metre run to the board.
2 guys coming down from Leicester crack of sparrow f**t to install expecting everything to be ready...
Regards
Steve
 
All installed now.
Blokes who installed it both had tanning parlours in Leicester. They reckoned just a couple of vents needed. No fan. Cabinets are used 6 mins at a time.
See how it goes, not the easiest place to install a ventilation duct.
Cheers Steve
 

Reply to Does a sunbed require RCD? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
I decided to get solar panels, the inverter instructions say one can use type AC, so the existing 14 x RCBO CU seems OK, may be a good idea to fit...
Replies
4
Views
1K
I’m a trainee electrician and would really appreciate the benefit of someone’s skill and experience on the following: Our house is a TN-C-S (100A...
Replies
70
Views
6K
  • Locked
united kingdom...yorkshire I rent a semi detached house out which was built 1970's With the tenancy just changed i thought i would change the...
Replies
44
Views
4K
Hello, I'm planning a small (500W) install with two panels and a dual micro-inverter (APS YC500i) and was hoping to get some advice. Before I...
Replies
2
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock