Discuss Domestic CUs have built in wiring of 16mm2 but... in the UK Electrical Forum area at ElectriciansForums.net

E

Eddiesparks

...what if you had a 100a cutout?!

So for e.g your tails (consumer and dist.) are both 25mm2 and you have a cutout fuse that is 100a - technically the cutout fuse is the only thing protecting from itself to the bottom of your mcbs. Most consumer units have the "built in" cables that are 16mm2 (from bottom of main switch to top of RCDs) - The CCC of these cables is 85/87ish amps so isnt that a problem?!

I'm curious!

Thanks

Ed
 
...what if you had a 100a cutout?!

So for e.g your tails (consumer and dist.) are both 25mm2 and you have a cutout fuse that is 100a - technically the cutout fuse is the only thing protecting from itself to the bottom of your mcbs. Most consumer units have the "built in" cables that are 16mm2 (from bottom of main switch to top of RCDs) - The CCC of these cables is 85/87ish amps so isnt that a problem?!

I'm curious!

Thanks

Ed

And the question is?
 
the CU tails are tri-rated and will withstand higher currents than the same csa of 7 strand, notwithstanding that they may have a higher max. temperature, which should be limited to the temp. rating of the main switch/RCD/s etc.
 
...what if you had a 100a cutout?!

So for e.g your tails (consumer and dist.) are both 25mm2 and you have a cutout fuse that is 100a - technically the cutout fuse is the only thing protecting from itself to the bottom of your mcbs. Most consumer units have the "built in" cables that are 16mm2 (from bottom of main switch to top of RCDs) - The CCC of these cables is 85/87ish amps so isnt that a problem?!

I'm curious!

Thanks

Ed
oh man!!
lol...lol...
what happens to current in parallel circuits eh eddie?
 
Your forgetting that their are normally doubled up sets, one set to each of the RCD units thus the load is shared down 2 sets of 16mm... as above the cable is tri-rated and unless you know the manufacturer then you cant gage its rating which well come down to 3 factors
-Core arrangement
-Size
-insulation
 
As above any wholesalers will supply it but its use may have restrictions like panel wiring etc as its insulation has differing properties...
 
have used tri-rated for meter tails in the past (coz. it was free from where i worked). bear in mind you need to fit crimps to the ends.
 
...what if you had a 100a cutout?!

So for e.g your tails (consumer and dist.) are both 25mm2 and you have a cutout fuse that is 100a - technically the cutout fuse is the only thing protecting from itself to the bottom of your mcbs. Most consumer units have the "built in" cables that are 16mm2 (from bottom of main switch to top of RCDs) - The CCC of these cables is 85/87ish amps so isnt that a problem?!

I'm curious!

Thanks

Ed

I wouldn't worry your head about it, not just because of the internal configuration of dual RCD CU's, but the fact you'll probably never see 100A being drawn through a typical domestic/commercial CU. ...I know that i never have, and not even close either!! lol!!
 

Reply to Domestic CUs have built in wiring of 16mm2 but... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Had UKPN come out to a property recently to upgrade the main fuse from 60A to 100A but when they arrived they said that the supply cable which he...
Replies
9
Views
2K
Hi, I'm a self-build amateur - I'll be running cables and getting system sign-off/inspection by certified competent person, and am just working...
Replies
6
Views
1K
B
inspected a job, service head 3p 4 wire. 100A BS88. meter tails 25mm2 ccc 101A out meter into 2 * henly blocks. out the henly blocks split into 2...
Replies
3
Views
2K
Guest55
G
O
I have just had a kitchen extension plus one living room built which will require wiring. In the original house there is a wire-fused consumer...
Replies
16
Views
3K
E
I think I've Posted this before, but I've just updated it. Some of the sparks where I work still get a little confused of what the different areas...
Replies
58
Views
77K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock