i am doing work in a void property for the council, there are downlights installed into a wet wall ceiling in the kitchen ( put in by previous tennant ) they are wanting to keep, when going round each downlight the earths were chopped away so went round sorted them all but i am getting no earth still so where they have joined from the original light position they have probably not joined the earth, the lights are wired through conduit with earths and the conduits earthed, and theres an earth going up to the light at the switch, i was wanting the ceiling down to get to the joint at the original light position but doing that would probably burst the wet wall and they would have to put a new ceiling up, the niceic inspector for the housing said that you can take a 4mm bond from the pipes in the boiler cupboard in the kitchen to the lights to give it an earth is this ok to do ?
 
I would try and get a CPC from the lights to the switch position if at all possible but if you can't then a 4mm to a suitable point to get continuity would suffice.

A note on the certificate and labels on the DB and CPC to make it easier for future works would also be advisable.
 
An extraneous conductive part maybe used as a protective conductor as long as it satisfies regulation 543.2.6.
Note a requirement is that the pipework is an extraneous conductive part and the cross sectional area shall be large enough or equal to applying regulation 543.1.1 which is sizing of protective conductors.

Best off reading regulation 543.2.1 and 543.2.6
 

Reply to Downlight earthing For housing in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all. Sort of an interesting one. I had a call from a client to say she is getting a shock when using the shower. I told her not to use it and...
Replies
15
Views
1K
I've wired some cable to a small 3x3 shed with 2 gpos, a 15a GPO, and a light. The shed is about 2m away from the house on a concrete slab. The...
Replies
0
Views
499
Hi All, I have just installed 8x GU10 downlights in our kitchen with a 2 way setup using the 2 cable method, when I turned the light on they are...
Replies
7
Views
1K
Hi all, Getting the utility room redone at this project house and the misses is absolutely adamant she wants downlights. Couple of reasons for...
Replies
26
Views
2K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock