Discuss Downsizing a cable mid-circuit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

DNS1

-
Esteemed
Reaction score
771
Seen this mentioned on a thread about cookers on the main forum. Someone asked about splitting a 10mm cable into 2 6mm cables to feed the oven and hob, but has been told it's not compliant.

Could someone point me in the direction of the regs about this one and some info on the theory behind it.

Many thanks!
 
433.2 is one of the sections in the BGB,

The 3M rule is why the circuit you mentioned in the other thread was not compliant.

ie. you need to suitably fuse/ocp down, within 3m, if you are going to change csa
 
Last edited:
This reg. can be extremely useful, especially in kitchens where you may need an additional supply for the likes of a cooker hood or a gas igniter
 
Ive had this before at CU change found10mm to cooker isolator 6mm to outlet then 6mm to cooker.I thought ok but wasnt 100% so asked Elecsa about this and was told ok no needed for any extra overload protection for smaller cable as long as smallest cable is rated for load which it was and make comment EIC.
Cheers
Neil
 
There’s also an interesting regulation (somewhere!) stating it’s OK to grossly downsize cable CSA, without protection, inside things like isolators and busbar chambers to feed small indicator lights etc. Clearly, fusing for this would be silly, and cable damage inside the chambers is unlikely.

That makes sense, since terminating say 25mm to a little neon lamp might be problematic :) Whenever I’ve installed such things I’ve deliberately used really thin cable which I reckoned would act as a fuse in itself, were say the lamp holder to go short circuit. Still feels iffy though.
 
Seen this mentioned on a thread about cookers on the main forum. Someone asked about splitting a 10mm cable into 2 6mm cables to feed the oven and hob, but has been told it's not compliant.

Could someone point me in the direction of the regs about this one and some info on the theory behind it.

Many thanks!

I see no reason why it cant be compliant.

Regards Chris
 
???? in what way ?, I agree it would depend on the OCPD at the origin of the 10mm cable, but reg. 433.2.1, 433.22 specifically mentions the requirements, as well as the "best practice guide" associated with the point of isolation being no more than 2m away.
 
???? in what way ?, I agree it would depend on the OCPD at the origin of the 10mm cable, but reg. 433.2.1, 433.22 specifically mentions the requirements, as well as the "best practice guide" associated with the point of isolation being no more than 2m away.

It does, so why can it not comply?
 
I may be missing something here Chris, but if the supply cable is 10mm, and is then split into (downsized) into two 6mm cables, one of them being 6m long with no forward ocpd within 3m, then how does this comply?
 
Lets say you run 10mm T&E on a 32mcb for x amount of meters then reduce the cable size to 6mm for the purposes of extending the run for 10m then according to 433.3.1(i) this is acceptable and exceeds the 3m everyone else is quoting 433.2.2, the one question no-one seems to have asked and is important in answering this OP is what size mcb is and the nature of the 10mm run.

433.2.2(ii) is very useful when looping 10mm tails from a henley block for a 1way board 45amp rated - and not having to commit to the 25mm tails as the cutout may require to do without this reg, the amount of time ive seen 16mm plus tails feeding into an isolator etc which has say a 20amp to 45amp mcb within is more than i can recall, the mcb upstream of the reduced tails prevents and overload been pulled through and as long as its within 3m is permitted.
 
Using reg 433.2.2 could you take a 6mm cooker cable ina dual connector and take out a 6mm to the cooker and a 2.5 cable to the cooker hood as long as the fcu is within 3m of the dual connector?
 
I can see the regs you are looking at, and agree the regs should not be taken in isolation.

Reg 433, says shall not be applied to installations situated in locations presenting a fire risk etc...

Iam sorry to have to disagree with both of you here, as a kitchen or other domestic location provides a very real risk of fire in my opinion.
You may be able to use that reg in a different environment and wiring system/containment system, other than domestic.

Iam not saying either of you are wrong per se, but I would not be happy signing that off, as I could not guarantee the conditions required to satisfy parts of 433.

I would much prefer to cover my own backside in this instance.

A very interesting debate none the less.
 
Last edited:
Using reg 433.2.2 could you take a 6mm cooker cable ina dual connector and take out a 6mm to the cooker and a 2.5 cable to the cooker hood as long as the fcu is within 3m of the dual connector?​

Yes it a very useful reg for this scenario.
 
I can see the regs you are looking at, and agree the regs should not be taken in isolation.

Reg 433, says shall not be applied to installations situated in locations presenting a fire risk etc...

Iam sorry to have to disagree with both of you here, as a kitchen or other domestic location provides a very real risk of fire in my opinion.
You may be able to use that reg in a different environment and wiring system/containment system, other than domestic.

Iam not saying either of you are wrong per se, but I would not be happy signing that off, as I could not guarantee the conditions required to satisfy parts of 433.

Working out the adiabatic may be the more sensible approach, but I would much prefer to cover my own backside in this instance.

A very interesting debate none the less.

I dont think a kitchen is what the regs term a location of fire risk or explosion.

How will the adiabatic help?
 

Reply to Downsizing a cable mid-circuit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

The electrician that installed my cooker circuit put in 10mm cable with a 32a fuse, a 45a cooker switch and 10mm cable to the backplate for behind...
Replies
12
Views
274
Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable...
Replies
9
Views
600
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
590
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
15
Views
520
I have just had my kitchen redone and the kitchen rewired with a new 6mm cable installed for an electric cooker. However I have changed my mind...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock